bluvac
i just recieved my bluvac yesterday ( friday 12-21-12) so i hooked it up to my vacuum pump several different ways everytime i isolate the pump the microns climb fast it goes over 1.000 microns in less than a minute. ill pull it down to about 110 microns then valve it off on many different tries. i put nylog on all the connections i even added another ball valve comming off the pump to ensure it wasnt the isolation valve built into the vac pump leaking. in all three setups in the pix maybe the gage itself is leaking or am i doing something wrong?? please help
-
12-22-2012, 01:33 PM #2
Couple things.
First, the BluVac will make you re-evaluate everything you think that you know about evacuation. It's THAT sensitive.
Second. In all of the arrangements that you're showing, the internal volume is very small, meaning that ANY leak will cause a rapid rise. Try evacuating a recovery cylinder or something else with a larger internal volume.
-
12-22-2012, 03:15 PM #3
Professional Member
- Join Date
- Jun 2012
- Location
- Fayetteville, NC
- Posts
- 117
The BluVac will frustrate your the first few times using it. It shows just how much your manifolds leak and it will have you buying the whole evac set up, which is definitely worth it. Like JP said pull it on a recovery cylinder.
-
12-22-2012, 05:10 PM #4
Professional Member
- Join Date
- Sep 2010
- Location
- miami,fl.
- Posts
- 320
-
12-23-2012, 08:01 PM #5
Professional Member
- Join Date
- Jan 2005
- Location
- Akron
- Posts
- 779
Anthony,
Everything that you have shown in the photos will leak a lot. Especially hoses and the vacuum pump blank off valve.
To get a stable vacuum and reasonable leak rate, first you need to have a volume. The smaller the volume, the faster it will indicate a leak. Second you need a better isolation valve like an Appion vacuum rated core tool, most ball valves are not vacuum rated. Third, use Nylog very sparingly. It is only intended to be an assembly lubricant. Excessive amounts will degas during evacuation and give the appearance of leaks. Also consider vacuum rated hoses for evacuation they will help a lot.
http://www.trutechtools.com/Vacuum-Training_c_1100.htmlJLB- Co Owner TruTech Tools Inc.
-
12-24-2012, 02:43 PM #6
The Bluvac will make your hair turn gray and fall out!!!
-
12-24-2012, 03:16 PM #7
Professional Member
- Join Date
- Jan 2005
- Location
- Akron
- Posts
- 779
It is not the BluVac but the leaks in your evacuation rig that you never knew you had that is frustrating. Eliminating those problems is what takes some hours now only minutes to do. Odd though you are correct, my hair is gray and falling out, I will have to contact the manufacturer Monday and see if it is related. Somehow if it is, I do not think I will get a straight answer.
JLB- Co Owner TruTech Tools Inc.
-
12-24-2012, 06:08 PM #8
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
-
12-24-2012, 06:27 PM #9
Professional Member
- Join Date
- Sep 2002
- Posts
- 717
-
12-24-2012, 06:33 PM #10
Professional Member
- Join Date
- Jan 2005
- Location
- Akron
- Posts
- 779
There are a few good units out there, I have tested a JB, Fieldpiece, Supco, Thermal, Yellow Jacket and the BluVac. Thermal and Yellow Jacket and BluVac all make a good high end gauge. Unlike most here I have actually had the opportunity to compare the micron gauges against a NIST rated vacuum gauge. There are several issues to contend with though, response, resolution, accuracy, temperature compensation, ability to use in low ambient temperatures, and ease of use, these even if you set cost aside. Also several are only accurate in a small segment of their range. Before the BluVac we only recommended the Thermal 14571 micron gauge as it was simply the best and most accurate gauge for the money. I still like that thermal simply for the analog qualities and the accuracy, and still use one in the shop. The BluVac however works a lot better in low ambients, has a back light, is much smaller and I like the response time and it is low cost. So yes for the money and the features, the BluVac is as good as it gets. The Thermal is a close second unless it is very cold, and the Yellow Jacket third simply because the units we tested were quite a bit off the NIST gauge until we were below 1000 microns. Below 1000 it was right on the money.
JLB- Co Owner TruTech Tools Inc.
-
12-24-2012, 06:33 PM #11
Professional Member
- Join Date
- Sep 2010
- Location
- miami,fl.
- Posts
- 320
-
12-24-2012, 06:39 PM #12
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
-
12-24-2012, 06:45 PM #13
Professional Member
- Join Date
- Sep 2010
- Location
- miami,fl.
- Posts
- 320
maybe you can answer my next question? im gonna pick up the evacuation kit from trutechtools. lets say on a reach in cooler/ice machines when you have to weigh in the charge and be as accurate as possible. i guess i can hook up the 2 appion core removal tools pull vacuum 500 microns or lower, valve off the core tools wait to make sure it holds. hook up my gages pull a vacuum on my hoses and manifols while the core tools are still closed then i can weigh in the charge. once i take my gages back off i would have to slide the cores back in. but with all that hooking up and taking off and purging it will screw up the charge im sure. or on something so small you just pull it through your maniflold and hoses. can i hear your answer or how you do it?????


Reply With Quote