    bluvac

    i just recieved my bluvac yesterday ( friday 12-21-12) so i hooked it up to my vacuum pump several different ways everytime i isolate the pump the microns climb fast it goes over 1.000 microns in less than a minute. ill pull it down to about 110 microns then valve it off on many different tries. i put nylog on all the connections i even added another ball valve comming off the pump to ensure it wasnt the isolation valve built into the vac pump leaking. in all three setups in the pix maybe the gage itself is leaking or am i doing something wrong?? please help
    Attached Images Attached Images    

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,547
    Couple things.

    First, the BluVac will make you re-evaluate everything you think that you know about evacuation. It's THAT sensitive.

    Second. In all of the arrangements that you're showing, the internal volume is very small, meaning that ANY leak will cause a rapid rise. Try evacuating a recovery cylinder or something else with a larger internal volume.

  3. #3
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    607
    Quote Originally Posted by jpsmith1cm View Post
    Couple things.

    First, the BluVac will make you re-evaluate everything you think that you know about evacuation. It's THAT sensitive.

    Second. In all of the arrangements that you're showing, the internal volume is very small, meaning that ANY leak will cause a rapid rise. Try evacuating a recovery cylinder or something else with a larger internal volume.
    maybe you can answer my next question? im gonna pick up the evacuation kit from trutechtools. lets say on a reach in cooler/ice machines when you have to weigh in the charge and be as accurate as possible. i guess i can hook up the 2 appion core removal tools pull vacuum 500 microns or lower, valve off the core tools wait to make sure it holds. hook up my gages pull a vacuum on my hoses and manifols while the core tools are still closed then i can weigh in the charge. once i take my gages back off i would have to slide the cores back in. but with all that hooking up and taking off and purging it will screw up the charge im sure. or on something so small you just pull it through your maniflold and hoses. can i hear your answer or how you do it?????

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,547
    Quote Originally Posted by anthonyac1 View Post
    maybe you can answer my next question? im gonna pick up the evacuation kit from trutechtools. lets say on a reach in cooler/ice machines when you have to weigh in the charge and be as accurate as possible. i guess i can hook up the 2 appion core removal tools pull vacuum 500 microns or lower, valve off the core tools wait to make sure it holds. hook up my gages pull a vacuum on my hoses and manifols while the core tools are still closed then i can weigh in the charge. once i take my gages back off i would have to slide the cores back in. but with all that hooking up and taking off and purging it will screw up the charge im sure. or on something so small you just pull it through your maniflold and hoses. can i hear your answer or how you do it?????
    That's exactly how I'd do it.

    I would add that, once I'm done with the initial charging, I'd re-install the cores, re-connect my gauges to the service ports, double check the charge by SH/SC and then seal the system back up.

  5. #5
    Join Date
    Jun 2012
    Location
    Fayetteville, NC
    Posts
    284
    The BluVac will frustrate your the first few times using it. It shows just how much your manifolds leak and it will have you buying the whole evac set up, which is definitely worth it. Like JP said pull it on a recovery cylinder.

  6. #6
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    607
    Quote Originally Posted by SgtBone View Post
    The BluVac will frustrate your the first few times using it. It shows just how much your manifolds leak and it will have you buying the whole evac set up, which is definitely worth it. Like JP said pull it on a recovery cylinder.
    i appreciate your replies, frustrated....... i was ready to slam it against the wall but i was strong enough not to i just put it all away and figured ill ask on here for help.
    sometime this weekend ill try it out on a tank.

  7. #7
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,115
    Anthony,

    Everything that you have shown in the photos will leak a lot. Especially hoses and the vacuum pump blank off valve.

    To get a stable vacuum and reasonable leak rate, first you need to have a volume. The smaller the volume, the faster it will indicate a leak. Second you need a better isolation valve like an Appion vacuum rated core tool, most ball valves are not vacuum rated. Third, use Nylog very sparingly. It is only intended to be an assembly lubricant. Excessive amounts will degas during evacuation and give the appearance of leaks. Also consider vacuum rated hoses for evacuation they will help a lot.

    http://www.trutechtools.com/Vacuum-Training_c_1100.html
    JLB,

  8. #8
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    607
    Quote Originally Posted by jim bergmann View Post
    Anthony,

    Everything that you have shown in the photos will leak a lot. Especially hoses and the vacuum pump blank off valve.

    To get a stable vacuum and reasonable leak rate, first you need to have a volume. The smaller the volume, the faster it will indicate a leak. Second you need a better isolation valve like an Appion vacuum rated core tool, most ball valves are not vacuum rated. Third, use Nylog very sparingly. It is only intended to be an assembly lubricant. Excessive amounts will degas during evacuation and give the appearance of leaks. Also consider vacuum rated hoses for evacuation they will help a lot.

    http://www.trutechtools.com/Vacuum-Training_c_1100.html
    hey jim, i appreciate your reply i wasnt trying to knock the bluvac i still have faith in it i heard so much good about it thats why i purchased it. im gonna pick up that evacuation kit.

  9. #9
    Join Date
    Oct 2010
    Location
    The very humid south
    Posts
    707
    The Bluvac will make your hair turn gray and fall out!!!

  10. #10
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,115
    Quote Originally Posted by acsolutionsllc View Post
    The Bluvac will make your hair turn gray and fall out!!!
    It is not the BluVac but the leaks in your evacuation rig that you never knew you had that is frustrating. Eliminating those problems is what takes some hours now only minutes to do. Odd though you are correct, my hair is gray and falling out, I will have to contact the manufacturer Monday and see if it is related. Somehow if it is, I do not think I will get a straight answer.
    JLB,

  11. #11
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,375
    Quote Originally Posted by jim bergmann View Post
    It is not the BluVac but the leaks in your evacuation rig that you never knew you had that is frustrating. Eliminating those problems is what takes some hours now only minutes to do. Odd though you are correct, my hair is gray and falling out, I will have to contact the manufacturer Monday and see if it is related. Somehow if it is, I do not think I will get a straight answer.
    Jim,do you think the bluevac is as good as it gets and all others microns gauges are junk and should not be trusted?, the mighty, magic bluevac hold the absolute true microns readings, right?

  12. #12
    Join Date
    Sep 2002
    Posts
    720
    Quote Originally Posted by valdelocc View Post
    Jim,do you think the bluevac is as good as it gets and all others microns gauges are junk and should not be trusted?, the mighty, magic bluevac hold the absolute true microns readings, right?
    I have never heard Jim Bergmann ever say that.

  13. #13
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,375
    Quote Originally Posted by Reeferman View Post
    I have never heard Jim Bergmann ever say that.
    that makes two of us! but by the nature of his comments seems like the bluevac is right and the rest of the vacuum gauges that dont behave bluevac like, are not to be trusted.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event