Found belt broken causing y2 to call and bring on mechanical. Thinking about adding an outdoor lockout to stop mechanical cooling from coming on as the compressor were a huge block if ice
-
12-24-2012, 06:42 PM #15[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
12-24-2012, 10:10 PM #16
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 916
Or a freeze stat.
-
12-24-2012, 10:43 PM #17
So true. Economizers have kept me very busy during the winter over the years. On many new accounts I often find enthalpy sensors disconnected with nothing else wrong. I tell young guys to learn about them because they generate work for the cold months when some get slow. I urge guys to not look at the controller and get overwhelmed. I tell them to break each circuit down and things get much less complicated. That is of course once they get an understanding of them
Sent from my SGH-T999 using Tapatalk 2
-
12-24-2012, 10:44 PM #18
-
12-25-2012, 08:41 AM #19[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
12-31-2012, 05:07 PM #20
Regular Guest
- Join Date
- Mar 2012
- Location
- Georgia
- Posts
- 20
Economizer would disable 1st stage mechanical cooling if outdoor conditions were suitable (sounds like they are) for free cooling. Suction line freeze stat on 2nd stage compressor or Low ambient thermostat for 2nd stage lockout. These units are not designed to protect the compressors from ANY unit malfunction.
Last edited by Cold shot; 12-31-2012 at 05:15 PM. Reason: incorrectly described the product that was being talked about.
-
01-01-2013, 09:04 AM #21
I can't say that I know of any design that "protects the compressors from any unit malfunction....."
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
01-01-2013, 01:48 PM #22
Regular Guest
- Join Date
- Mar 2012
- Location
- Georgia
- Posts
- 20
True, but there are several things that can be added. Air proving switch, freeze stat, low & high pressure switches, discharge line thermostats, phase monitors. All to protect the compressor.
-
01-01-2013, 01:54 PM #23[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
01-15-2013, 09:02 PM #24## + years in the field never made you a know-it-all
This industry is far more diverse than you are
-
01-15-2013, 09:46 PM #25
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
I always shake my head when I see a economizer installed but never hooked up.