    Trane YCD036D manual?

    Does anyone have a link to the maintenance manual for the YCD series RTU? I'm having a hell of a time finding anything online.

    Any useful Trane troubleshooting guides would be helpful......

  2. #2
    Join Date
    May 2010
    Location
    Canada
    Posts
    1,223
    Post Likes
    Thread Starter
    I'm just trying to get a copy of the book that comes with the unit and can find anything at all online. The stat is flashing "E1" which is heating failure. The unit wont fire ( combustion motor wont even start ) in test mode. I only had a couple minutes last night to troubleshoot because they were closing. The unit had no book or wiring diagram ( none of the units did ). I quickly changed out the relay and ignition control board with a unit that was working and still no go.

  3. #3
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    6,032
    Post Likes
    Did you check for voltage at the motor?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  4. #4
    Join Date
    Oct 2007
    Location
    Maine
    Posts
    12
    Post Likes
    If there is voltage at the motor try to give it a spin. Sometimes these ones freeze in place.

  5. #5
    Join Date
    May 2010
    Location
    Canada
    Posts
    1,223
    Post Likes
    Thread Starter
    Ok so here is what Happened. My ampmeter was reading ohms, capacitance, and amps but had failed on voltage. There was voltage to the motor but my meter let me down.

    Thanks for the help.

  6. #6
    Join Date
    Mar 2008
    Posts
    284
    Post Likes
    Quote Originally Posted by eddiegoodfellar View Post
    Ok so here is what Happened. My ampmeter was reading ohms, capacitance, and amps but had failed on voltage. There was voltage to the motor but my meter let me down.

    Thanks for the help.
    Sent u a pm message here got some more info on this

    Sent from my BlackBerry using Tapatalk please excuse typographical errors
    If you can not do it right, Why even do it at all?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.