Page 2 of 2 FirstFirst 12
Results 14 to 21 of 21
  1. #14
    Join Date
    Dec 2012
    Location
    Columbus OH
    Posts
    32
    Post Likes
    If you are rea lconcerned with the oil issue you can add a oil level saftey switch to the unit.
    Regards

  2. #15
    Join Date
    May 2004
    Location
    Galveston, Texas
    Posts
    62
    Post Likes
    Thread Starter
    A oil safety switch would be an idea but if the oil gets low and it shuts off then lost product is a serious issue.

    On the topic of oil seperators, I know that they are not 100% but wouldn't what little oil that made it through come back easier since its not turning into a large blob with the rest.

    Would the bulletproof route be use a oil separator like a helical or coalescent the feed into a oil level controller like a Parker PL60CH. That way the oil level will be the same in crankcase even if a slug comes in?

    I still plan on swapping out riser with 5/8" but would like the oil level pretty close to bullet proof.

    Thoughts ?

  3. #16
    Join Date
    Apr 2010
    Location
    San Diego, CA
    Posts
    229
    Post Likes
    Quote Originally Posted by foxtrot View Post
    On the topic of oil seperators, I know that they are not 100% but wouldn't what little oil that made it through come back easier since its not turning into a large blob with the rest.
    In a word, no.

    Longer answer -I work on a lot of systems that run low and ultra low temps on 507. All with oil separators. What oil does get through the separator just sits out there until it builds up enough to get pushed back to the compressor in a rush after an off cycle. If your off cycles aren't bringing all the oil back now, they won't bring it back with a separator installed.

  4. #17
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,513
    Post Likes
    Quote Originally Posted by cmclifton View Post
    What oil does get through the separator just sits out there until it builds up enough to get pushed back to the compressor in a rush after an off cycle. If your off cycles aren't bringing all the oil back now, they won't bring it back with a separator installed.
    Words of wisdom.
    If the only tool you have is a hammer, you tend to see every problem as a nail. – Abraham Maslow

  5. #18
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    733
    Post Likes
    I don't believe you have an issue with oil return, if it ran a week.

    You maybe are seeing it, just before defrost.

    We run r-507 exclusively in low temp application (-40 sst) without oil return issues.


    what is the box temp you are after?

  6. #19
    Join Date
    May 2004
    Location
    Galveston, Texas
    Posts
    62
    Post Likes
    Thread Starter
    Just a negative -10F freezer, nothing extreme.

  7. #20
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    733
    Post Likes
    checking on PMs should be good enough for now.

  8. #21
    Join Date
    Jul 2001
    Location
    Gold Coast of Connecticut
    Posts
    4,860
    Post Likes
    What temperature are you running the box. I bet at -30 evaporator the load is 6K or less. You may need a 5/8" suction or warm up the box. Be sure your super-heat is on the money to keep the load up.

    I would leave it as is.
    Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.