Results 1 to 1 of 1
12-20-2012, 11:42 AM #1
- Jan 2004
- Northern California
- 73
Johnson Controls TEC-2002-4 Wireless Thermostats Niagara AX
Hello All,
I have a building with 8 TEC-2002-4 Wireless Thermostats and an FX-60 Supervisor with Tridium Niagara. When someone puts a thermostat into Local Occupancy at the stat it stays in Local Occupancy until I manually override the system to Unoccupied in Niagara AX. The Override time in the thermostat program is set to 3 hours and I have the Lockout set to 1 which is partial lockout.
First I'm wondering if I possibly have something set wrong on the thermostats.
Second I'm wondering if there is a way to set up custom programming in Niagara AX that clears the Local Occupancy Override every night so I can at least start fresh the next day. The thermostats do have schedules in Niagara that are unoccupied most of the time but these of course are a lower priority than Local Occupancy. Is there a way to change this??
A little info on the thermostat settings:
Heating is limited to 75 degrees
Cooling is limited to 70 degrees
Overrides are set for 3 hours
Comm addresses are 4, 5, 6, 7, 8, 9, 10, 11 starting with heatpump 1
Pan ID is set to 1
Channel is set to 15
Reversing Valve Operation is set to 0
Number of Stages is set to 1
Thank you!