I am having a ducted split unit of 11 TR. I have already done the cooling load calculations for my room but now I have to calculat the dehumidifier capacity as per requirement. The factors I am considering in calculations are:
1. Infiltration load
2. human load
3. ventilation load(fresh air ventilation load and door opening load)
are there any other factors that I should consider while calculating the dehumidifier capacity??
Infiltration load=humidity diff. b/w outside and inside *density of air * space volume * some factor
Human load=no. of people * factor
Ventilation load= fresh air load + door opening load
fresh air load=fresh air quantity * humidity diff. * density
door opening load=area of door* time(sec)door staying open * no. of openings
Any remarks plz reply.
ty
Consider the building materials ability to allow moisture diffusion from oustide. Also consider the internal moisture load from activities.
The a/c is able to provide dehumidification only when there is sensible cooling loads. In most cases, supplemental dehumidication needed for the periods when there is low/no sensible cooling loads.
Units like the Ultra-Aire dehumidifiers have latent only with sensible reheat. Ultra-Aire has the high latent cooling and a small amount of sensible cooling.
Regards TB