Closed Thread
Page 1 of 2 12 LastLast
Results 1 to 20 of 21

Thread: Using a Bacharach Fyrite Tech 50

  1. #1
    Join Date
    Dec 2012
    Location
    Mahwah NJ
    Posts
    1,219
    Post Likes

    Using a Bacharach Fyrite Tech 50

    I just bought a Fyrite Tech 50 and am using it on an older Burnam oil fired boiler which has a newish Beckett burner installed. I get visible smoke unless I have about 18% or more excess air which yields about 84% efficiency.

    My understanding is one can tune for higher flame efficiency which results in more smoke which will soot up the boiler decreasing heat transfer efficiency which greatly reduces overall efficiency. It sounds like going for zero smoke is the way to go.

    Do my numbers and thinking sound about right?

    Thanks!
    Greg
    Quick reply to this message Reply  

  2. #2
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,430
    Post Likes
    sounds like a tech to tech question.

    I've always understood zero - 1 smoke is preferred with the burnham oil fired burners, but i don't do a lot of oil work.
    Quick reply to this message Reply  

  3. #3
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Dont worry about the efficiency the meter tells you because it's lying. set it up with 0-1 smoke and 4-7% o2
    Quick reply to this message Reply  

  4. #4
    Join Date
    Dec 2012
    Location
    Mahwah NJ
    Posts
    1,219
    Post Likes
    Thread Starter
    Quote Originally Posted by gravity View Post
    Dont worry about the efficiency the meter tells you because it's lying. set it up with 0-1 smoke and 4-7% o2
    Thanks! I need to get a smoke tester. I'll go for 7% o2 to be safe.

    Greg
    Quick reply to this message Reply  

  5. #5
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,430
    Post Likes
    last one I did, manual was specking 11% CO2. probably best to get a manual for the specific equipment you're working on.
    Quick reply to this message Reply  

  6. #6
    Join Date
    Dec 2012
    Location
    Mahwah NJ
    Posts
    1,219
    Post Likes
    Thread Starter
    Quote Originally Posted by 71CHOPS View Post
    last one I did, manual was specking 11% CO2. probably best to get a manual for the specific equipment you're working on.
    Thanks. Would you say I should get the manual for the burner, boiler, or both? I'm guessing only for the burner.

    Greg
    Quick reply to this message Reply  

  7. #7
    Join Date
    Jul 2012
    Location
    Upstate NY
    Posts
    295
    Post Likes
    I would get a manual for both but more so the boiler should tell you what it wants the burner to run at most of the time. Sometimes the burner manuals will tell you that but not always.
    Quick reply to this message Reply  

  8. #8
    Join Date
    Dec 2012
    Location
    Mahwah NJ
    Posts
    1,219
    Post Likes
    Thread Starter
    Quote Originally Posted by wicat3 View Post
    I would get a manual for both but more so the boiler should tell you what it wants the burner to run at most of the time. Sometimes the burner manuals will tell you that but not always.
    Thanks! I'll do that.

    One thing I've been doing that's sort-of-a-smoke-test is to plug the sampling hole with a piece of aluminum foil (tin foil for you old folks). There's a piece of the aluminum foil plug that sticks into the stack. After a day of running pull that plug out and look at the part that sticks into the stack. If it's clean, you've got zero smoke. I call it the "Gregorio method" in case I'm making history here.

    Greg
    Quick reply to this message Reply  

  9. #9
    Join Date
    Jul 2012
    Location
    Upstate NY
    Posts
    295
    Post Likes
    Im sure that works just fine but Personally I would Use testing equipment. By letting it run without knowing what its set up for you run a risk of hurting someone or even killing someone. They make the equipment to testing for a reason.
    Quick reply to this message Reply  

  10. #10
    Join Date
    Dec 2012
    Location
    Mahwah NJ
    Posts
    1,219
    Post Likes
    Thread Starter
    Quote Originally Posted by wicat3 View Post
    Im sure that works just fine but Personally I would Use testing equipment. By letting it run without knowing what its set up for you run a risk of hurting someone or even killing someone. They make the equipment to testing for a reason.
    I know what you mean. I just hate to spend another hundred dollars.

    Thanks for your help! I really love these forums. It is so kind and helpful for all of the people who are experts to pass along their knowledge to others to come asking.

    I hope you all have a very happy holiday season!

    Greg
    Quick reply to this message Reply  

  11. #11
    Join Date
    Jul 2012
    Location
    Upstate NY
    Posts
    295
    Post Likes
    No problem. Rather see things get done right then hacked in and have someone get injured an all. Good luck
    Quick reply to this message Reply  

  12. #12
    Join Date
    Dec 2012
    Location
    Mahwah NJ
    Posts
    1,219
    Post Likes
    Thread Starter
    Quote Originally Posted by wicat3 View Post
    No problem. Rather see things get done right then hacked in and have someone get injured an all. Good luck
    Thanks to everyone who posted.

    Here's the follow up.

    After reading what you guys wrote, and then talking with a tech at Beckett, I was convinced to get a smoke test kit. There are no shortcuts to be taken. It has proven to be invaluable. The fellow at Beckett said the smoke test kit is the most important piece of test equipment. So I found an inexpensive one and it was very revealing. You can't see the difference between a #1 and a zero smoke by looking at what's coming out of the stack. Looking for soot on the aluminum foil plug I put in the sampling hole wasn't accurate either. The smoke test kit showed me immediately when I got to zero smoke. The readings on the Bacharach Fyrite 50 show:

    O2 7.6
    CO2 10
    Excess Air 53%
    Efficiency 81.5

    I can get the efficiency up to 82 and maybe a bit more only at the expense of smoke so it's not worth it.

    I really think that between the two pieces of gear, the smoke tester is the most important one if you had to pick just one. You adjust the burner using the smoke test kit. The Bacharach is nice because you can see the numbers and not just wonder what you're getting.

    Thanks guys. My real life experience and time on the forums has taught me to really listen to the guys in the know.

    Greg
    Quick reply to this message Reply  

  13. #13
    Join Date
    Apr 2011
    Location
    Coastal Maine
    Posts
    1,092
    Post Likes
    Dude, if your having to run 53% excess air to get a 0 - Trace smoke, then you have something else going on. Those numbers look horrible for just about any Beckett oil burner. What was your stack temp and CO at light off and shut off? I would bet that you have flame impingement going on. Are you a pro? What specific equipment is this? What nozzle size are we talking about?
    Quick reply to this message Reply  

  14. #14
    Join Date
    Dec 2012
    Location
    Mahwah NJ
    Posts
    1,219
    Post Likes
    Thread Starter
    Quote Originally Posted by meplumber View Post
    Dude, if your having to run 53% excess air to get a 0 - Trace smoke, then you have something else going on. Those numbers look horrible for just about any Beckett oil burner. What was your stack temp and CO at light off and shut off? I would bet that you have flame impingement going on. Are you a pro? What specific equipment is this? What nozzle size are we talking about?
    First things first, I'm not a pro. But keep in mind the "pros" around here want to come and charge hundreds of dollars to put in a new filter and photocell and maybe ignitor tips. Most "pros" don't even want to brush and clean the boiler. We have a guy that's one of the better ones, who does brush and vacuum the boiler, and he didn't bring any of his test equipment even though he was called because the boiler was smoking. He just adjusted it by eye and promised me I could borrow his Bacharach kit, a promise he never kept. His girl that answers the phone said "he can't loan the Bacharach kit, he needs it to adjust burners when he goes out on calls!". Somehow that he didn't adjust mine was lost on her. So I bought my own gear.

    No, there's no impingement.

    I have no idea what the nozzle size is since I didn't replace it.

    It's an old Burnham boiler and new-ish Beckett burner.

    It doesn't run long even in cold weather. I think it's doing pretty good.

    If you have any suggestions I'd love to hear them.

    Thanks for posting!

    Greg
    Quick reply to this message Reply  

  15. #15
    Join Date
    Apr 2011
    Location
    Coastal Maine
    Posts
    1,092
    Post Likes
    Well, anyone who shows up to work on any combustion equipment without a Combustion Analyzer is not a pro, he is a hack. Period.

    As to your setup, there are a lot of things that could cause your readings, but since your not a pro, I am not going to get into it. The reasons we charge what we charge is because it is worth it.
    Quick reply to this message Reply  

  16. #16
    Join Date
    Dec 2012
    Location
    Mahwah NJ
    Posts
    1,219
    Post Likes
    Thread Starter
    Quote Originally Posted by meplumber View Post
    Well, anyone who shows up to work on any combustion equipment without a Combustion Analyzer is not a pro, he is a hack. Period.

    As to your setup, there are a lot of things that could cause your readings, but since your not a pro, I am not going to get into it. The reasons we charge what we charge is because it is worth it.
    Well thanks for telling me what I already knew, and not telling me what I need to know. I know some boards are for pros only. I thought this one was for everyone. If it's not a place for people like me to look for help you should say so. Then we won't waste each other's time.

    Greg
    Quick reply to this message Reply  

  17. #17
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Quote Originally Posted by takoateli View Post
    Well thanks for telling me what I already knew, and not telling me what I need to know. I know some boards are for pros only. I thought this one was for everyone. If it's not a place for people like me to look for help you should say so. Then we won't waste each other's time.

    Greg
    The site rules clearly say no DIY allowed. It is unfortunate that you are having trouble finding a company in your area to properly adjust your unit. Make a point to specifically ask for CA service, check the map on this site for someone in your area, if no one is, call every company within driving distance and make your request.
    Quick reply to this message Reply  

  18. #18
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by takoateli View Post
    Well thanks for telling me what I already knew, and not telling me what I need to know. I know some boards are for pros only. I thought this one was for everyone. If it's not a place for people like me to look for help you should say so. Then we won't waste each other's time.

    Greg
    If you had read the rules when you registered you would have read that this site is for pros only. Others are welcome but won't receive technical help.
    Quick reply to this message Reply  

  19. #19
    Join Date
    Dec 2012
    Location
    Mahwah NJ
    Posts
    1,219
    Post Likes
    Thread Starter
    Quote Originally Posted by mason View Post
    The site rules clearly say no DIY allowed. It is unfortunate that you are having trouble finding a company in your area to properly adjust your unit. Make a point to specifically ask for CA service, check the map on this site for someone in your area, if no one is, call every company within driving distance and make your request.
    OK, I missed that it's no DIY. I'll leave you pros to have your circle jerk. Maybe the forum admin can delete my account.
    Quick reply to this message Reply  

  20. #20
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Quote Originally Posted by takoateli View Post
    I'll leave you pros to have your circle jerk
    Will you come back and get in the middle... always need a pivot man.

    Seriously though, lots of non "pros" get help on this site but there is no DIY since it puts you in danger of harming yourself or your equipment, as you have already demonstrated with almost leaving your unit improperly tuned and possibly with a more serious issue not being addressed.

    No offense need be taken, the rules are the rules.
    Quick reply to this message Reply  

Closed Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •