    No room to remove blower motor

    We have an air handler installed with the ductwork 12 inches from the access panel. Because its so close, the blower assembly cannot be removed and there is no way to sneak around to loosen the collar on back of the cage.

    I want to avoid removing the section of duct so the next best thing is to cut hole in rear panel then cover with ductmate sandwich door.

    I'd like to get some other ideas. Help !!

    Anthony

  2. #2
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    1,277
    Is it in a attic, crawl space, mechanical room or closet? Describe the install a little better. Pictures would help a ton!

    Over the summer, I had a 2 year old 3 ton split with a faulty TXV. Problem was that you couldn't access the coil at all. So, I quoted the customer to remove the AHU, replaced TXV, and then reinstall with correct service access. We got the job.

  3. #3
    Join Date
    Dec 2008
    Location
    Ontario Canada
    Posts
    534
    The way most furnace blowers are set up, getting the blower to slide out the back would be quite difficult

    It's tough without pics, but could you cut a section of duct and re-fit so it could be taken in and out with relative ease in the future?

    Post pics on WOS?

  4. #4
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    2,747
    I did one this summer , same scenereo , no room to get blower out .

    I just looosened blower assembly ,let it fall into the bottom of cabinet , then layed on my side and reached inside cabinet to work to remove motor.

    What a pain in the ass that was

  5. #5
    Join Date
    Jan 2008
    Location
    s chester county,pa
    Posts
    144
    send duct designer/installer to replace fan and do duct mods.
    then fire said individuals.
    that would be too easy i guess. how about a modular blower assembly flipped on the outlet side of the ahu? if it would be service accessible. sometimes you gotta think out of the box.

  6. #6
    Thanks all. I'll try to get some pictures today.

    No thoughts on making a 10x6 access hole in the back of the cabinet so I can reach the collar on the blower motor?

  7. #7
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,619
    just cut the duct out of the way

    if it's easy access to back side for set screw hole- knock your self out.

    but:
    1-crap like that should have never been installed

    2-apparently the "codes" there don't cover or define easy access

    3-find what ever butt head put that in and try to beat some understanding into them
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  8. #8
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    3,948
    Normally when you see crap like this its when the lowest bidder got the job. You get called out because the customer got a disconnected message when they tried to call the original installer back..

  9. #9
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    15,506
    Quote Originally Posted by Snapperhead View Post
    I did one this summer , same scenereo , no room to get blower out .

    I just looosened blower assembly ,let it fall into the bottom of cabinet , then layed on my side and reached inside cabinet to work to remove motor.

    What a pain in the ass that was
    How do you do this when the blower assembly is on a rail/slide in type? It has one direction, slides out the front, not back, not down, and of course not up.
    __________________________________________________ ____________________________
    “Reality is merely an illusion, albeit a very persistent one.” –Albert Einstein

    “Experience is a hard teacher because she gives the test first, the lesson afterwards.”-Vernon Law

  10. #10
    Join Date
    Oct 2002
    Posts
    1,135
    No reason not to cut access hole in cabinet, if you want. Won't hurt.

    Often wonder why there is no hand hole access to blowers using new electronic ECM motors. Had to change just the electronc s mounted at the end of the motor. Why should it take 30 minutes to pull a blower just to troubleshoot when you could reach in the access hole and be done in 5 minutes.

  11. #11
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    1,934
    Quote Originally Posted by timjimbob View Post
    No reason not to cut access hole in cabinet, if you want. Won't hurt.

    Often wonder why there is no hand hole access to blowers using new electronic ECM motors. Had to change just the electronc s mounted at the end of the motor. Why should it take 30 minutes to pull a blower just to troubleshoot when you could reach in the access hole and be done in 5 minutes.
    If I have a choice of which side I bring the return air into it's always to the motor side. There goes the factory hand hole access.

    I'll take having to remove a blower assembly any day compared to how hard it is to get to some of the old ignitors and how many (were installed with no thought about having to be removed) items had to be moved just to get my hand near it.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  12. #12
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,018
    Just remove the duct. It's usually not as difficult as you might think. Bite the bullet and "getter done"!
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com

  13. #13
    Join Date
    Aug 2012
    Location
    MN
    Posts
    77
    Cut duct and reinstall with canvas peice to make quick work next time

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event