r-22 mcquay chiller
I'm new at working on chillers. I 'm working on an older Mcquay high pressure chiller that has no Freon in it. Some of the guys say there is a leak in the evaporator barrel. There is water running through the barrel. Will water get into the refrigerate system. I'm willing to learn teach me.
-
12-19-2012, 10:12 PM #2
Moved to chillers forum.
-
12-20-2012, 09:20 PM #3
While I can appreciate your wanting to learn chillers " Baptism by fire" at this point is not the time or place to do it. There are far too many variables to deal with in your case. The best educational idea I can give you is to call a well seasoned tech, stand back and take good notes. -GEO
Of all the things I have lost in my life, I miss my mind the most-GEO
-
12-24-2012, 08:37 PM #4
Professional Member
- Join Date
- Jul 2008
- Location
- Metro Atlanta
- Posts
- 69
To answer your question directly, water will only enter the refrigerant circuit if the pressure on the water side is greater than the pressure on the refrigerant side. If the refrigerant has completely leaked out, water has likely made its way in there. Like GA1279 said, there are MANY things to consider here. An eddy current needs to be done to determine the integrity of the tubes in the evap barrel. You can plug tubes if they are compromised, any then leak check the system again. You'll likely have to change the oil in the compressor, im assuming they are old recipe, and then evacuate the system to remove the rest of the moisture. This will be expensive for the customer, make sure you have the resources before taking on a job like this one.
-
12-26-2012, 09:59 AM #5
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105
I can't help but wonder why "some of the guys" aren't teaching you. Are they not experienced on chillers, either?
-
12-28-2012, 01:04 AM #6
-
12-30-2012, 06:08 PM #7
Are "those guys" that say evap is leaking guessing? I would put nitrogen in and leak search before I assume chiller barrel is leaking. How long has the chiller been down?
-
12-30-2012, 06:21 PM #8
-
12-30-2012, 07:27 PM #9
-
01-02-2013, 09:23 PM #10
Regular Guest
- Join Date
- Dec 2012
- Posts
- 7
sorry guys for not getting back faster. found a leak at sight glass made repair. about the leak in the evap. barrel. I leak checked with nitrogen 100 psig for one hour. no drop in pressure. pulled vacuum down to 700 micron let set over night raised back to 730 micron the next morning. get me on the right track PLEASE.
-
01-02-2013, 09:26 PM #11
the right track is learning before you go into action..... hope all worked out for you....
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
01-02-2013, 11:04 PM #12
U should try to pull the circuit down below 500 microns. If u can't get it below 500 u might have leak or contamination in the system. How big is the chiller or the circuit u are working on ?
RTFM!!!
-
01-02-2013, 11:47 PM #13
agreed. go lower. below 500 microns is better but lower is best. lower and holding is an even better proof to a non leaking system. keep in mind that some things leak under a vacuum and some things leak under pressure so continue to leak check. since this is a unit that has had a lot of issues, you need to keep going until you checked everything several times and then several times again.
The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.