    I am trying to figure out why a furnace keeps blowing 40 amp time delay fuses. It has 2 heating elements at 14 and 14.5 ohms each, I also pulled them out and visually inspected. The blower spins freely and the capacitor has 300 + volts. Each leg is pulling 35 amps when both elements are energized at 248 volts. It will run for about 15 to 30 minutes before it blows the fuse. The transformer was humming really loud so I replaced it. I don't know what else to check.
    Sep 2009
    Marietta, GA
    Shouldn't you have a 60 amp on there? How many KW are the heating elements in total?
    Probably cause they are a bit under sized for the continuous load they are on. If you didn't include the blower in your amp check. Check it, and you'll see your close to 40 amps. If you included the blower motor amp draw in your reading, then you need a 45 amp fuse, 50 if blower not included(based on 8.6KW of strip heat).
    Dec 2003
    Code requires the heating circuits to be fused at 125% of load, this calls for 30amp protection for each 5 KW of heating element.
    Aug 2012
    Tulsa, OK
    Thanks for the replies, there are two elements at 3.5 kw each. I got the amp reading(35 amps) from each of the lines coming in. I checked the current through one element and it was around 15 amps and the fan was pulling 1.5 amps. The name plate calls for 40 amp over current protection and it is on a 40 amp breaker.
    Southeastern Pa
    Five posts and no one has asked this....???????
    ARE YOU A TECH?
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Aug 2012
    Tulsa, OK
    Yes sir, brand new though. Don't know what else to check.
    are all the line voltage connections tight?
    is there anything flopping around near the elements?
    are the fuse clips tight?
    Jul 2010
    Eastern Kentucky
    Sounds like loose connection somewhere. I would get someone more experienced to check it with you ,no use in taking chance of burning house down due to wire getting too hot
    Southeastern Pa
    Quote Originally Posted by hvacMartinez View Post
    Okay, then.
    Work on getting your post count up to 15 so you can apply for Pro membership. It's free, and it will allow you access to the educational forums and the Pro Technical forums, where we really dig into technical problems. We stay pretty vague out here in the open, as the search engines index these pages.
    On the equipment label, you should see a listing for the maximum overcurrent device. Did you see that value?
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Aug 2012
    Tulsa, OK
    I checked all the connections and everything is tight. While I was doing that I noticed that the fuses were really hot. The fuses fit tightly, is it possible the disconnect is loose and that is what is causing it to get hot and causing the fuse to blow? Should I replace the disconnect?
    Jan 2005
    Emerald Coast
    Is the cooling coil very clean?
    Do not attempt vast projects with
    half vast experience and ideas.
    Southeastern Pa
    The test for the disconnect is that when the connections are together, and the unit is under its normal operating load (in this case, making heat) you look for a voltage drop across the disconnect.