    Nov 2012
    Upstate NY
    Tracer VAS Setup Problem
    I have an IntelliPak RTU with cooling only, coupled with VariTrane VAVs (Comm3/Comm4), that are defined in Tracer Summit as a VAS. The system behaves properly in all respects but one.
    When in Unoccupied mode (controlled by schedule), after a few hours with RTU and all VAVs in "unoccupied" mode:
    1. The VAV units go into Night Heat/Cool mode to heat (all 8 of them, within a 1 hr. period, once it'sw cold enough)
    2. The VAV units open their air valves & heating coils to heat
    3. The VAS's AHU Fan Request = 'ON'
    4. The RTU's Present Value = Night Heat/Cool
    5. The RTU's Active Mode = Unoccupied Cooling (the RTU is cooling only)
    6. RTU Fan will not run.
    Not sure what I've missed, but any help would be grreatly appreciated.
    Mount Airy, MD
    Thread relocated to "Controls"
    Apr 2005
    Boulder,CO.
    Try a simple CPL program that will tell the RTU to go to Opt Start this will control the fan on keep OA Damper closed. ie:
    PROGRAM NIGHT_HEAT_COOL
    DEFINT Night_Heat_Cool
    DEFOBJ RTU, VAS
    /// This program controls the Present Value of an I-PAK to OPT/START
    /// If the Present Value of the vas is night heat cool
    ///Routine Execution: This program is executed every minute.
    ///Routine Text File:night_heat_cool.CPL
    RTU = {Retreat Bldg RTU}
    VAS = {Retreat VAS}
    IF (VAS.{Present Value} = 8)
    THEN
    CONTROL ({Retreat Bldg RTU}, {Present Value}, 1, 5, SET)
    ELSE
    CONTROL ({Retreat Bldg RTU}, {Present Value}, 1, 5, RELEASE)
    END IF
    END
    Nov 2012
    Upstate NY
    Many thanks!!!! I will try when the site re-opens after Xmas. I have to ask, though, why does the Summit application not do this on its own? Seems to me to be a fairly basic feature that most HVAC applications would want. I mean, why does the VAS application activate the AHU Fan Request = 'ON' if it's not going to actually activate the fan?
    Jul 2001
    maryland
    Your description of what's going on makes me wonder what's controlling the RTU to "Night Heat/Cool", I've never seen VAS control to 'night heat.cool' so I wonder if Area is taking control of the RTU and it's not responding because it's 'cooling only'.
    Saving the world...one service call at a time.