Thread: Hiel H9mpd075
-
12-19-2012, 01:00 AM #14
i would be looking real hard at the new bad inducer/wheel or secondary h/x
-
12-19-2012, 04:55 PM #15
Is the draft steady? Check with a manometer or draft gauge of your choice and post the readings.
Someone else raised the question of a plugged heat exchanger but I would expect that would be a continuous problem rather than an intermittent one.
I just converted a new ICP furnace to LP yesterday. It was the first time I had to put screws in the burners as directed in the instructions. It was a new model and a new style conversion kit. The conversion went smoothly though.
-
12-19-2012, 08:12 PM #16
Professional Member
- Join Date
- Dec 2011
- Location
- missouri
- Posts
- 135
Could the manifold be cocked, or twisted, not allowing the orifices to point straight into the burners? Just a thought, let us know what you find!
-
12-19-2012, 09:21 PM #17
Professional Member*
- Join Date
- Jul 2010
- Location
- wisconsin
- Posts
- 248
You were vague in your description of the series of events. Did you arrive at the house for a no heat call and find a bad inducer motor, and then have the burner issue, or was the burner issue present before you replaced the inducer? Also, check the colector box, as ive found three of these cracked in the past. I would install mixing screws in the burner venturi anyways to see if it changes anything.
-
12-20-2012, 09:51 AM #18
Regular Guest
- Join Date
- Dec 2003
- Posts
- 46
You are right I should have started at the begining. The inducer had been installed by another service tech (who is no longer doing service work), about a month before I was called. This was replaced the homeowner said because the old one seized. His call to me was because the furnace started making what he called a ratteling noise. When I tried the furnace I found the problem with the flame burning inside the venturi of the burners, this caused the door on the front of the burner compartment to vibrate until the flame jumped to front of the burners. Upon inspection I found 3 cracks in the collector box (Hiel calls it the transition assy), I sealed those with hi-temp RTV silicone with no change in the flame at startup. I ordered a new trans. assy and installed it, and checked the tubes of the secondary heat exchanger at that time, (all were clear). That brings me back to the points in my original post.
-
12-20-2012, 09:26 PM #19
Regular Guest
- Join Date
- Jul 2012
- Location
- Cincinnati ohio
- Posts
- 103
Have you checked the pressure in the combustion box? I remembered I had a similar issue on a mobile home furnace with a combustion air restriction.