    AuCS cleaning system

    Anyone have experience with the Manitowac AuCS auto cleaning system?
    Experience is what you have an hour after you need it.

  2. #2
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Some..... Wasup
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  3. #3
    Join Date
    Feb 2004
    Location
    Western New York
    Posts
    1,199
    Post Likes
    Thread Starter
    Have a college where I'm bidding a new ice machine. In this particular building, they only treat the hot water, and the water is heavy in calcium. Just wondering if the system works well in this application. No other minerals, just heavy calcium.

    For some reason they are not interested in water treatment.
    Experience is what you have an hour after you need it.

  4. #4
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    It would do more for an I series than any other IMO. On a older unit it wouldn't do much for cleaning the sensors. Since the redesign it would do more for you as far as keeping the important parts clean and working. Anywhere there is splashing or not in the water pump flow will not be cleaned by an AuCS.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #5
    Join Date
    Feb 2004
    Location
    Western New York
    Posts
    1,199
    Post Likes
    Thread Starter
    Thanks for the input I-man.
    Experience is what you have an hour after you need it.

  6. #6
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    FWIW Every time I see one it is empty
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  7. #7
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    Quote Originally Posted by itsiceman View Post
    It would do more for an I series than any other IMO. On a older unit it wouldn't do much for cleaning the sensors. Since the redesign it would do more for you as far as keeping the important parts clean and working. Anywhere there is splashing or not in the water pump flow will not be cleaned by an AuCS.
    Exactly my thought. Sadly though the only I series I've seen was at a United branch or the seminar. I've maintained plenty in the past with AUCS, filling them periodically at which point the ice thickness probe would be removed and cleaned. Slime is a whole different beast which will plague a machine regardless.

    Sent from my SCH-I800 using Tapatalk 2

  8. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    From what I have seen since we took on restaraunt work, the aucs units have not worked in some time, and the chain is not interested in any maintnance, only failure mode service calls.

  9. #9
    Join Date
    Feb 2004
    Location
    Western New York
    Posts
    1,199
    Post Likes
    Thread Starter
    I hear you- yesterday I went to a ski center to get the ice machines going. All Mani's with the Everpure systems bypassed. 3 out of 4 machines down due to scale. Go figure.

    But back to my original question, if the aucs system is maintained, does it handle scale on the I series?
    Experience is what you have an hour after you need it.

  10. #10
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Bet it would. The water probe seems to attract scale right at the tips like a magnet with the new electronics and the ITP could probably have anything hanging off of it and still work.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  11. #11
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    Isn't the I pretty much an S aside from the ITP technology and the digital panel/interface?

    Sent from my SGH-T999 using Tapatalk 2

  12. #12
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Water level is all new too! Had the least problems with scale/slime shutting down Q series!
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  13. #13
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    They do well on most of the water side. They will keep scale off of evap and distribution system. They will not clean thickness probes. Keep them full and clean your probe regularly and they are a good thing IMO. For scale that is. At a subway or pizza shop they are useless. PS seperate your drain lines.

  14. #14
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Tommy knocker View Post
    PS seperate your drain lines.
    I'm not sure exactly what you mean by that...
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  15. #15
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    The head drain and the bin drain. Usually one of the first things I have to do on new accounts. If you don't and they have auto clean the cleaner and removed scale end up in the bin.

  16. #16
    Join Date
    Aug 2010
    Location
    Garland, TX
    Posts
    39
    Post Likes
    There is also a drain for the head on the I series, different from the pump out drain. There is a service communicator on it. So the heads have two different drains. The I series are a completely different beast from the S. The mechanics are the same but the machine has soo much more technology. I feel that they blow the Prodigy out of the water on this one.

  17. #17
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Tommy knocker View Post
    The head drain and the bin drain. Usually one of the first things I have to do on new accounts. If you don't and they have auto clean the cleaner and removed scale end up in the bin.
    I have always seen them run separately, that's why I asked.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  18. #18
    Join Date
    Jun 2012
    Posts
    117
    Post Likes
    There is also a drain for the head on the I series, different from the pump out drain. There is a service communicator on it. So the heads have two different drains. The I series are a completely different beast from the S. The mechanics are the same but the machine has soo much more technology. I feel that they blow the Prodigy out of the water on this one.
    Yeah, but with all the technology, they still can't get them to run worth a d*mn. I just had another service call this week with an ice thickness probe popsickle going on

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •