    Looking for opinion. Less than 10 yr old forced hot air oil burner. It starts, gets to 130 degrees, fan kicks on. as it cools and gets near 80deg. it satarts to sputter and the burner just goes out the fan will still blow.
    Has a brand new fan/limit. clean out by heat exchanger was cleaned. Input appreciated!

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,870
    Possible cracked heat exchanger.

    Call a tech to inspect it.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Jun 2003
    Location
    New Hampshire
    Posts
    2,666
    Oil burner sputtering after a few minutes of run time usually means a clogged oil filter or oil line or pump strainer or a combination of all three.
    As far as cracked heat exchangers go a positive fire oil burner with a cracked heat exchanger won't necessarily cause a sputtering.
    It will cause a very high over fire pressure in the burner box and sooting, but the burner will probably continue to run.

    [Edited by oil lp man on 11-25-2006 at 04:54 PM]

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,870
    He said when it starts to cool back down.

    I took this for the first fan cycle.

    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Nov 2000
    Location
    Lancaster, Pennsylvania
    Posts
    884

    My input..........

    call a oil burner technician to come out and diagnose the problem. If you have a cracked heat exchanger, this is not a condition that you want to put off.
    KX500......the original big green meanie

  6. #6
    Join Date
    Nov 2006
    Location
    Gloucester Virginia
    Posts
    20

    Hmm

    I agree with lp man sounds like starvation for fuel!! A crack will not usually cause the burner to shut down but will cause a lot of sooting and high temp over flame with pressurization of chamber sometimes. Anyway you look at it a service call is in order..
    heattech

    If it hasnt worked properly since you serviced it last then why did it take the customer 2 years to complain??

  7. #7
    Join Date
    Nov 2004
    Location
    Naples, Fla.
    Posts
    1,403
    I've seen simular events with water in the oil --- have your tech dbl ck.

  8. #8
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    2,003
    You didn't say if the burner would come back on by itself once it'd done this. If it does then the problem SHOULDN'T be with anything dealing with the oil or the burner itself. The safety control on the oil burners are designed to be a one time shot requiring manual reset if it detects a problem with the operation of the burner. This reset should only be done by a qualified service person as fuel oil has the capability, under certain circumstances, to cause rather impressive explosions with parts flying off the furnace.
    In any case you need to call a qualified oil service company to come out and give your entire system a good going over.

  9. #9
    Join Date
    Nov 2006
    Posts
    2
    I put off changing the filter for the tank shut off valve was screwed. Fixed that today, changed filter and replaced nozzle and BINGO so far so good..... she's running!
    Thanks all who spent the time to stop by my post. Your opinions had me decide to start with the easiest fix first.
    Cheers!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event