Thread: Old 10 Seer Coil and new 13 Seer Cond- OK ?

  1. #1
    Join Date
    Nov 2006
    Posts
    7
    Post Likes
    Lennox 4 ton 10 Seer compressor has failed. 10ACB48-5P 1997
    Can I install a new Rheem 3.5 ton 13 Seer condensing unit?
    The Coil is Lennox 4 ton 10 Seer CB29M-51-1P with a balancing valve. Thanks.

  2. #2
    Join Date
    Nov 2006
    Location
    Oregon
    Posts
    853
    Post Likes
    Most of the pros will tell you to change HP and Coil at the same time. It's not wise to try and salvage an old coil during a HP failure.

    For piece of mind I'd do coil + linset + HP.

    If the compressor self destructed you could have contaminents thruout the system.


  3. #3
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    3,039
    Post Likes
    Originally posted by g2345w
    Lennox 4 ton 10 Seer compressor has failed. 10ACB48-5P 1997
    Can I install a new Rheem 3.5 ton 13 Seer condensing unit?
    The Coil is Lennox 4 ton 10 Seer CB29M-51-1P with a balancing valve. Thanks.
    Indoor and outdoor systems should be matched for max efficiency and reliability. It is highly likely that you will experience compressor failures in the future that can be directly contributed to the mismatch. There will be no Rheem warranty on the outdoor unit if the indoor is not a rated match. Change the system in it's entirety.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  4. #4
    Join Date
    Jan 2005
    Location
    35 miles from Tunica (casinos)
    Posts
    152
    Post Likes
    I concur with above posts. You did not state how compressor failed. ) a system replacement should be MATCHED PERIOD. Why send money to achieve eficiency and destroy it with a mis-matched system?


    I'm just old not senile

  5. #5
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Hey guys, its not a heat pump, its straight AC.

    Ideally you should change both, and considder going to a heat pump.

    The CB29 air handlers were not strictly for 10 SEER outdoor units, and it is even on the list of indoor units Lennox says it is ok to match several of thier current outdoor units with.

    I know some here don't agree with the practice, but with a straight AC condensor, correctly installed with filter driers and proper evacuation, and a TXV in the indoor coil, the system would work.
    It probably won't be 13 SEER, and may be just a little less than cooling capacity than with a matching indoor unit, but it will work. There isn't really any reason it would be less reliable either.

    It gets a bit more sticky with heat pumps. If you want to have a heat pump outdoor unit installed, but are not in a position to change the indoor unit, you should stick with one of the heat pumps Lennox says it is OK to match with that air handler.

    I'll probably catch some heat for the above statements.


  6. #6
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    i agree with mark on this
    even tho a matched system is the idael way to go
    the cb29 i blieve came with a factorie installed txv
    if it didnt then have one put in

  7. #7
    Join Date
    Nov 2006
    Posts
    7
    Post Likes
    Thread Starter
    Yes Mark, the local installers say they frequently install new 13 seer condensing units on old 10 seer coils, just as long as they have a TVX.
    What do you think of dropping from 4 to 3.5 ton on the condenser? The load calc says 43,000 and the system cycles off even on hot days. Does this help or hurt the mismatch?
    Does anybody know WHY the compressor could fail? Any comments on pressure, humidity, or cfms? Thanks to all of you for your comments, George.


  8. #8
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    43,000 btuh eh? That the total or the sensable? The sensable load is the important one when it comes to picking equipment.

    Most compressor failures are caused by contaminants in the refrigerant, poor indoor airflow, other installation problems, or a combination.

  9. #9
    Join Date
    Nov 2006
    Posts
    7
    Post Likes
    Thread Starter
    Update from George !

    Existing Coil- 4 ton 10 Seer
    Prooposed Condenser- 3.5 ton 13 Seer

    http://www.heatload.com says 43,727 TOTAL btu.
    Sorry, No breakdown is given on sensible vs latent.

    We're in South Padre Island, Texas and as you might guess, summers are hot, humid and long. It's 9:27pm and 72 degrees. Bet you wish you were here, as we got 7 nice trout today.

    Heat calc stats- Frequent high 95. Summer low 77
    Frequent low 45 Winter high 73
    Temp differential 20 (75 degrees)
    Grains 63

    We'd like the system to run more for more stable temperature and lower humidity. Mismatching the SEER will reduce efficiency?, and mismatching the size will give longer runtimes? How does this mismatch effect the humidity issue?


  10. #10
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    3,039
    Post Likes
    There could still be warranty issues connecting a Rheem condenser to the older Lennox A/H. If Lennox has ratings for this indoor unit with 13 Seer outdoor your best option in the long run would be to stick with Lennox. The technician onsite would have the best information available to offer an educated guess on the cause of the compressor failure. Low airflow, lightening strikes, loose wires, short cycling, refrigerant undercharge or overcharge, bad capacitor, poor installation practices originally etc. are some conditions that could have caused compressor failure.

    Using your load calc have the system capacity matched for sensible and latent loads. You will be happier when it's 95°and 95% humid.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  11. #11
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    3,039
    Post Likes
    Pay the $50 and use HVAC-Calc from this site. It will give a breakdown of sensible and latent loads.

    This is a dilemma with mis-matched systems. You are guessing at efficiency and capacity split.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    The 3.5 ton condenser may not be able to get the indoor coil cold enough to remove anymore, or as much moisture as the 4 ton did.
    Can the indoor blower be slowed down.
    Have to be carefull not to slow it sown too much also.

  13. #13
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    As others have metnioned, The problem with mismatching straight air is you dont know what capacity you will get. The system determines this, not just the outdoor coil... SO what if the homeowners system barely kept the house at 95, and your frankensystem loses 2-3k btuhs? You gonna sit there and warranty parts and labor trying to get it to work? Slowing th fan might make up latent, but it will reduce sensible. I wouldnt even try to guess at what you are starting with.

    What are you going to do if the efficiency actually drops? And yes, it can. If you end up with a system that costs more to run than the original system, you will have to somehow explain it.

    Be a pro and offer a proper solution.

  14. #14
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,047
    Post Likes
    How old is this system?

    If you don't want to spend the money to replace the indoor coil, how about just getting a new compressor?

    There's no point of getting a new condenser if it's going to consume close to as much energy as a 10 SEER.

    Doing it right will cost you less in the long run, even with financing if you can't afford the upfront price. (repairs, energy consumption)

    Just remember that the next compressor will be doomed to fail if the underlying problem is not found and corrected.

  15. #15
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Plug in that air handler model number into the ARI search.
    The Lennox 13ACD-042, 048 and 060 are all current production lennox condensing units, and the Lennox 13HPD-042 and 048 are current production heat pumps that are ARI rated with the CB29M-51 air handler. The matchups get right around 12 SEER.

  16. #16
    Join Date
    Nov 2006
    Posts
    7
    Post Likes
    Thread Starter

    Smile Update- Conclusion

    Lennox commercial support transferred me to a systems design engineer. He said the 10 SEER air handler is compatible with the 13 SEER condenser and will yielded 12 SEER in their testing. The engineer was very knowledgeable on the issue and also pleasant and helpful. Thanks Lennox, and my forum friends, the install cools well and we are hopeful that annual electric costs will reflect some savings. Thanks, G

  17. #17
    Join Date
    Jun 2004
    Posts
    247
    Post Likes
    I think if you actually measured the 4 ton coil you'd see the surface area, fpi and number of tubes is very close to a 3.5 ton, 13 SEER coil. Most higher SEER coils are simply bigger heat exchangers with a TXV added. That's why you're close to 12 SEER, IMHO

  18. #18
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    what unit did you end up getting?

  19. #19
    Join Date
    Jun 2007
    Posts
    2
    Post Likes
    The evaporator coils I have worked on in the past have had capillary tubes. How do you install the TXV as the one's I've seen just have an inlet and outlet?

  20. #20
    Join Date
    Aug 2004
    Location
    Florida, Kentucky, Michigan, Ohio, Arizona, Colorado, Nevada, and Califormia
    Posts
    410
    Post Likes
    I'm w/ Mark on this as well. We have done many of the cb's this way. The Lennonx supplied expansion valve has a bleed so the pressures equalize and a start assist is not needed. Those Lennox coils also already have a schraeder on the suction line just for that txv bleed... just remove the existing metering device, add a couple of adjustable wrenches and there you go.. it will only go in one way. Something not mentioned though..if you don't already have a digital stat I'd recommend buying one. The inherent time delay in the stat will allow complete equalization between cycles. Yes the txv bleed allows for equalization, but it doesn't happen as quickly as it would w/ a piston... unless the unit has a scroll.. then you're ok.
    "Surprised ?! If I woke up tomorrow with my head sewn to the carpet, I wouldn't be more surprised."
    Clark Griswold

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •