Thread: Lennox SL280v vs. Goodman GMVC8

  1. #1
    Join Date
    Nov 2012
    Posts
    52
    Post Likes

    Lennox SL280v vs. Goodman GMVC8

    Hey all. My brother is looking to replace his 10 yr old furnace in his 2200 sq. ft. 1 story house with an unfinished basement that's 1000 sq. ft. He lives very close to me around the Atlanta GA metro area. The current furnace is a Lennox G40UH 90,000 BTU input. The A/C was replaced 1 year ago and it is a Goodman GSX13 that's a 3 ton (36,000 BTU) along with new indoor coil.

    So far he was given 3 quotes and we narrowed it down to 2:

    Quote #1: Lennox SL280UH090V36B along with new Honeywell visionpro IAQ thermostat. Some ductwork replacement will be needed as well.

    Quote #2: Goodman GMVC80604B*B. Contractor said that thermostat is fine and can work on two stage and a w2 wire will be added (thermostat is Honeywell RTH6450B that was installed the same time as the new A/C).

    These did come from two separate companies and the one recommending the Goodman did a manual j. The other contractor said that the current size was fine. I'm surprised none of the companies quoted me on 90% furnaces.

    Install matters more than brand, but it's the features of these furnaces that is throwing me off. The Lennox, according to Lennox's website, says it has "silent comfort technology". Could this mean that the Goodman is louder? My brother really wants a quiet furnace compared to the current one. I trust both companies though, and they are both well known in my area. What do you think we should go with? Thanks in advance.

  2. #2
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,086
    Post Likes
    Why is the current furnace being replaced?
    Beware of advice given by some guy on the Internet.

  3. #3
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    No way a 2k sqft house in atl needs a 90kbtu furnace. I'd go with the one that did a manual j. 10 year old furnace shouldn't need replacing. I'm sure goodman has an x13 or ECM furnace as well which is why they claim to be quieter, which I disagree. Proper ducting produces quiet, efficient, comfortable and long lasting systems not a blower motor.

  4. #4
    Join Date
    Nov 2012
    Posts
    52
    Post Likes
    Thread Starter
    Quote Originally Posted by Milk man View Post
    Why is the current furnace being replaced?
    He just wants to upgrade to 2 stage. The current furnace is cycling on and off to much (4-5 minutes on, 15-20 minutes off) and he wants to have 2 stage so that it will run loner, provide more even temps throughout the house, and he wants to feel more comfortable. He wants the feature of variable speed so that it can help with dehumidification in the summer time. The company recommending the Goodman is saying the current furnace is "oversized" for 2200 sq ft. That's why they quoted him on 70,000 BTU.

  5. #5
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,086
    Post Likes
    Quote Originally Posted by jtrammel View Post
    No way a 2k sqft house in atl needs a 90kbtu furnace. I'd go with the one that did a manual j. 10 year old furnace shouldn't need replacing. I'm sure goodman has an x13 or ECM furnace as well which is why they claim to be quieter, which I disagree. Proper ducting produces quiet, efficient, comfortable and long lasting systems not a blower motor.
    I thought burner noise. What noise is objectionable?
    Beware of advice given by some guy on the Internet.

  6. #6
    Join Date
    Nov 2012
    Posts
    52
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    No way a 2k sqft house in atl needs a 90kbtu furnace. I'd go with the one that did a manual j. 10 year old furnace shouldn't need replacing. I'm sure goodman has an x13 or ECM furnace as well which is why they claim to be quieter, which I disagree. Proper ducting produces quiet, efficient, comfortable and long lasting systems not a blower motor.
    Thanks. I agree that a 10 year old furnace should not need replacing. I talked him out of replacing, and he kinda ignored what I said. The inducer in the current furnace is overheating and running at high amps. This was discovered during a heating tune-up back in November. The tech said that the inducer will eventually fail in the near future. Obviously I don't understand why my brother won't just have the inducer replaced instead of the whole furnace.

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by jtrammel View Post
    No way a 2k sqft house in atl needs a 90kbtu furnace. I'd go with the one that did a manual j. 10 year old furnace shouldn't need replacing. I'm sure goodman has an x13 or ECM furnace as well which is why they claim to be quieter, which I disagree. Proper ducting produces quiet, efficient, comfortable and long lasting systems not a blower motor.
    The GMVC80604B is a VS ECM blower. And sounds much closer to the size furnace that a 2200 sq ft home in his area would need.

  8. #8
    Join Date
    Nov 2012
    Posts
    52
    Post Likes
    Thread Starter
    I think the reason why the current furnace is short cycling is because it is oversized. That is also one of the reasons why my brother wants to upgrade. Another company is coming out tomorrow to give another estimate and they are a Trane dealer. I'll give an update on how it goes.

  9. #9
    Join Date
    Nov 2012
    Posts
    52
    Post Likes
    Thread Starter
    Update... The Trane dealer came today and quoted the following:

    Quote #1: Trane XC95m model# TUHMB080ACV3VA along with new thermostat

    Quote #2: Trane XV80 model# TUD2B060A9V3VA. New thermostat is optional.

    Some ductwork will need upgrading. This is the only company that quoted a 90% furnace. It seems to me that the XC95m is an overkill for Atlanta. What do you think? This company did do a manual j and spent a great amount of time evaluating the system and ductwork.

    After talking to my brother a few minutes ago on the phone, we decided that we will probably throw out the Lennox quotes. This will leave us deciding between Goodman and Trane. The price was higher for the Trane than the others. Install matters more, but I trust both companies which is making this decision more difficult. Which route should we go with? Thank you in advance.

  10. #10
    Join Date
    Nov 2012
    Posts
    52
    Post Likes
    Thread Starter
    As for Goodman furnaces, I heard that their burner operation is very noisy and sound like a jet engine. Is this true??

  11. #11
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    double post

  12. #12
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    If a 36,000 BTU A/C will cool that house in Atlanta I think a 40K furnace is plenty of heat. IMHO if you live south of the mason-dixon line buy the smallest furnace that has enough blower capacity for the AC. You can buy 40k furnaces with 3 ton blowers. If a 40K won't keep a house in Atlanta warm some SERIOUS air sealing/ductwork repairs need to be done.

  13. #13
    Join Date
    Nov 2012
    Posts
    52
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    If a 36,000 BTU A/C will cool that house in Atlanta I think a 40K furnace is plenty of heat. IMHO if you live south of the mason-dixon line buy the smallest furnace that has enough blower capacity for the AC. You can buy 40k furnaces with 3 ton blowers. If a 40K won't keep a house in Atlanta warm some SERIOUS air sealing/ductwork repairs need to be done.
    Thanks for the input. My brother lives north of that line. The Goodman furnace that he was quoted on is the smallest size it comes in. This will mean 42,000 BTU input on low fire and 60,000 input on high fire for this certain model, correct?

  14. #14
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by J8500 View Post
    Thanks for the input. My brother lives north of that line. The Goodman furnace that he was quoted on is the smallest size it comes in. This will mean 42,000 BTU input on low fire and 60,000 input on high fire for this certain model, correct?
    Didn't you say he was near Atlanta in the 1st post? I must have misread something. If he is in Atlanta the payback time on a 90%+ furnace vs. an 80% furnace will be VERY long unless gas prices spike. If his annual heating bill is $500 and he saves $50/mo by getting the 90% furnace it will take years before it pays off. I can see springing for the variable speed blower in a southern climate...

  15. #15
    Join Date
    Nov 2012
    Posts
    52
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    Didn't you say he was near Atlanta in the 1st post? I must have misread something. If he is in Atlanta the payback time on a 90%+ furnace vs. an 80% furnace will be VERY long unless gas prices spike. If his annual heating bill is $500 and he saves $50/mo by getting the 90% furnace it will take years before it pays off. I can see springing for the variable speed blower in a southern climate...
    I did mention that in the first post. Variable speed can help control the humidity though, and I can see why it can be needed in a southern climate (mainly on the A/C side). Thanks for the info. 80% probably sounds more ideal for the Atlanta area. My brother will make final decision probably this afternoon.

  16. #16
    Join Date
    Nov 2012
    Posts
    52
    Post Likes
    Thread Starter
    Merry Christmas and Happy Holidays.

    After several days of thinking over the estimates, my brother settled on the company quoting the Goodman GMVC8. He trusted this contractor the most and the price was pretty good. The install is set for the end of next week and so far we don't have anymore questions to ask. Thanks for all your advice and take care!

  17. #17
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    It's sad that Manufacturers force you to oversize the furnace or go to a 90% in order to get the variable speed blower.. A 45k is perfect for most Southern installations that only require 3 tons of cooling. The 2nd stage of the 60k could be left unhooked and the homeowner would never know the difference.

  18. #18
    Join Date
    Nov 2012
    Posts
    52
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    It's sad that Manufacturers force you to oversize the furnace or go to a 90% in order to get the variable speed blower.. A 45k is perfect for most Southern installations that only require 3 tons of cooling. The 2nd stage of the 60k could be left unhooked and the homeowner would never know the difference.
    The contractor did say that the installers will allow the furnace to only run in first stage because 60k is oversized.

  19. #19
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Rheem and Ruud are the only manufacturers that I've seen offering a 45k furnace with a variable speed blower, but you have to upgrade to the 95% 2 stage furnace to get it.. Part of me even wonders if variable speed is worth it in a primarily cooling climate. A 45K 80% 2 stage with a PSC motor may offer just as much comfort at a lower cost.

  20. #20
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by 54regcab View Post
    Rheem and Ruud are the only manufacturers that I've seen offering a 45k furnace with a variable speed blower, but you have to upgrade to the 95% 2 stage furnace to get it.. Part of me even wonders if variable speed is worth it in a primarily cooling climate. A 45K 80% 2 stage with a PSC motor may offer just as much comfort at a lower cost.
    VS blower is valuable in a primarily cooling area, if they want good humidity control also.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •