Results 1 to 13 of 13
Thread: Clamp meters
    Jul 2012
    Cincinnati ohio
    Clamp meters
    I am looking for a meter that is capable of reading compressor starting amps. I have a fieldpiece and a uei and neither of them have a peak option. Is there another way to check it or is the meter just not capable?
    I've seen meters with a peak hold feature. I forget the brand at the moment.
    Why do you need to measure this?
    Dec 2012
    columbus, OH
    i would say to test staring amps on motors
    Fluke 336,376,381.
    In a machine room
    The Fieldpiece SC56 does that.
    California
    I use the SC56
    Dec 2012
    columbus, OH
    stupid emos the uei p r o : dl379
    Dec 2012
    columbus, OH
    i have a UEI PROL379 it will hold min/max on any setting amp volts temp ohms and will also work with any feildpeice head attachment
    Jul 2012
    Cincinnati ohio
    Quote Originally Posted by Core_d View Post
    I have that meter but it doesn't hold the starting amps only run....unless I am doing something wrong. if so tips are welcome.
    Quote Originally Posted by 2141 View Post
    You need to set the range first so it isn't in auto ranging mode otherwise you get out of range stored as a max.
    Central NJ Area
    I have a Fluke 376 with the flexible amp probe. Works great and also has a min/max/average feature you desire.
    Hampton Roads, Virginia
    Check out this information on in-rush measurement.
    http://support.fluke.com/find-sales/...629920_a_w.pdf
    Kevin
    "There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria
    "It's not the customer's job to know what they want." -- Steve Jobs
    S.E. Pa
    Fieldpiece SC77 does everything you need in one slim, sturdy compact meter.
