3 Ton Rheem AH With A 2.5 Ton Goodman Condenser
I just had a new Rheem 3.0 ton air handler installed(Clasic RHSL-HM3617JA), I have a 2.5 ton Goodman condenser outside(13 seer 4 years old) both r-22. The Rheem has a 2.5 ton TXV installed not a 3.0 ton. I am on the beach in SC and the ac is not getting cold enough and the heat pump heat is not very warm. The rheem replaced my old Carrier 3 ton and my repair guy is saying it is fine get used to it.
Can anyone help? Does the TXV need to be a 3 ton? Another HVAC contractor that came out out said the 2.5 TXV was not allowing enough Freon through for the fan speed, which is on low... but still pretty high, he said get more advise??? Thanks In Advance!!!!
-
12-15-2012, 02:02 PM #2
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,749
-
12-15-2012, 02:14 PM #3
What makes you say the txv is 2.5 ton?
Also the indoor valve size has no effect on the unit in heat mode.
It sounds like it could have a bad valve in cooling which would not surprise me. They are susceptible to damage.
-
12-15-2012, 02:23 PM #4
New Guest
- Join Date
- Dec 2012
- Posts
- 3
The contractor that came out looked at the number on the TXV and said it is a 2.5. on the heat pump mode doesnt the system rum backwards?? so wouldn't that also control how warm the coil got? it get warm when the electric heat kicks in.
-
12-15-2012, 02:43 PM #5
The indoor txv has no affect on heating and is supposed to bypass.
1. You have a mismatched system-which is not a good thing to have with a heatpump system: Were you warned about this when the airhandler was replaced?
2. Rheem/Ruud equipment is typically engineered to be very less forgiving when mismatched with other manufacturers in my experience. they typically only play well together.
See if there are any contractors in your area from our locator....It's not the Brand with the fewest repairs-It's all in the install!!! Attention to detail and using the best materials!
-
12-15-2012, 03:11 PM #6
RHSL has 410 TXV
Sent from my HTC VLE_U using Tapatalk 2
-
12-15-2012, 05:03 PM #7
New Guest
- Join Date
- Dec 2012
- Posts
- 3
Was not warned... I wish i was. I opened the unit and checked the TXV says 30 on it so it does match the 2.5 ton condenser outside. The issue is really the cooling side, the fan speed seems high on this unit even though it is on low the cool air out of the vents is just not cold, it is more like cool. This is what worries me if I wait until spring and summer i will have no recoarse.
So the fan speed is on low, when they put the guages on outside they said that it was fine.... but not really cold air. Any thoughts??
-
12-15-2012, 05:59 PM #8
That air handler is fine for 2.5 or 3 ton unit but won't work if your outdoor unit is R22
Sent from my HTC VLE_U using Tapatalk 2
-
12-15-2012, 06:11 PM #9
Post all the numbers that are on the TXV. They may not have put the R22 TXV in.
-
12-15-2012, 07:31 PM #10
RHSL-HM3617JA is a 3 ton R410a air handler. Won't work w/ your R22 condenser unless they swap in a R22 TXV- which I'd advise agains't.
Best match would be that R410a AH & a new matched Rheem R410a HP condenser. Mismatched gear rarely works well- even more so on heat pumps.Always drink upstream from the herd
-
12-15-2012, 07:35 PM #11
Your compressor wont live long either if its a r410a txv.
-