    EER & SEER

    Many if not all Geo-systems are rated using using EER, why not Seasonal also?
    Always here

  2. #2
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    6,345
    Bc the ground is ~the same temp all year so there are no seasons down there just consistency.

  3. #3
    Join Date
    Jul 2007
    Location
    Delaware
    Posts
    3,824
    So we can have the same EER as a geo.

  4. #4
    Join Date
    Apr 2012
    Location
    Georgetown Delaware
    Posts
    197
    Quote Originally Posted by jtrammel View Post
    Bc the ground is ~the same temp all year so there are no seasons down there just consistency.
    Your ground water remains constant, as in a pump and dump. A closed loop does not remain constant. To answer the original question.... I ave had it explained to me a half dozen times and it allways involves a equation for conversion. Way above my pay grade.
    Eric
    Eric Sackett
    weberwelldrilling.com
    Delta P= 8 ATA
    www.youtube.com/weberwelldrilling

  5. #5
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    1,942
    Quote Originally Posted by energy star View Post
    So we can have the same EER as a geo.
    What do you mean by that?

    Think of it this way on a heat pump COP is how efficient it is at a given temperature(47degrees for air source) and HSPF is the seasonal average. So if a system has an HSPF of 9 divide by 3.413 and it has an average COP of 2.63

    SEER and EER are a but more difficult. EER is still an efficiency at a given temperature if I remember correctly its about 82 degrees outdoor with 78 indoor temps and 1 EER means 1 watt of energy removes 1 BTU of heat.

    So back to your question, air source could have the same EER but with geo systems rated up to 41 EER and air source having up to 14 or 15 EER there is a long way to go.
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  6. #6
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    It's actually a complicated issue since any heat pump, water or air source loses capacity and efficiency as the temperature drops or flow is reduced on the source cooling fluid...whether air or water.

    If we're talking dual fuel for example, a air source heat pump above 45F can have COP's up around 4.... not far from geothermal. Similarly, EER at 60F on a higher effciency air soruce unit can approach 20.

    So it's one of those "it depends" answers. The more research I do, the more I realize that delivered efficincy on both system can vary widely. That's why a good installer is so, so improtant, and absolutely critical on geothermal.

    A EER or 41 is a COP of 12. That's just crazy. Non inverter water ot water cna get pretty high too under the right conditions.