    Heat pump Acid test.

    I found this in a heat pump the other day, and a custom cage.

    I don't think this will be fun to change out, nor easy.
    Attached Images Attached Images   
    The opinions expressed by me are not that of my employer.


    insulation modern marvels
    http://www.youtube.com/watch?v=g37riSkyZzM

  2. #2
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,018
    Why the cage?
    Did you do a acid test because the compressor was shot?

  3. #3
    Join Date
    Jan 2011
    Location
    Metro Atlanta
    Posts
    790
    Not sure why the cage, it's in a park that is heavily patrolled by park rangers, county and local police. I have not been at this park without seeing a cop car.

    I got there and the breaker was tripped. I reset it and it popped again. I went to test the capacitor to see if it was bad, and it was. i went and got a new one, reset the breaker and it popped again, tested the compressor and got OL from C to S and C to R, but got 2.3 from R to S.

    I took an Acid test to see if there was Acid in the system so when I changed it out I would not kill the new one.
    The opinions expressed by me are not that of my employer.


    insulation modern marvels
    http://www.youtube.com/watch?v=g37riSkyZzM

  4. #4
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,018
    OK. I only asked because I wasn't sure if you were checking the acid for some other reason.
    Have you done a clean up on a system before? I'm curious what people are doing for clean ups now days. Back when I was doing them we installed liquid and suction filters, new refrigerant and then returned a month later to check the acid level and pressure drop of the filter and do a second clean up if necessary.

  5. #5
    Join Date
    Mar 2012
    Location
    Georgia
    Posts
    21
    I use Acid Away & install suction & liquid line replaceable core driers w/ HH cores. Run system for a couple days, remove suction core, replace liquid line core drier with standard core drier & run a acid/moisture test. Also, always find out WHAT CAUSED THE COMPRESSOR FAILURE! There are too many technicians replacing compressors without finding out what caused the failure. Lastly, always replace the starting components with the compressor replacement.

  6. #6
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,051
    Did you really need a strip for that ne? Wheew

  7. #7
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,018
    Quote Originally Posted by SBKold View Post
    Did you really need a strip for that ne? Wheew
    What?

  8. #8
    Join Date
    Jan 2011
    Location
    Metro Atlanta
    Posts
    790
    I will be putting in a Scavenger, and liquid and suction filter.

    I did this one time before on a straight AC, not a heat pump.

    On that one I blew the lines, flushed it, blew it again, put liquid and suction filters on and that was it, never hand another issue with that compressor.

    I am also use to working on ruud units, I am sure that job will be 1000 times easier than this job will be. I will need a ladder to get in, and out of this unit, or hang upside down. I love Ruud Premium units, they are so easy to service.
    The opinions expressed by me are not that of my employer.


    insulation modern marvels
    http://www.youtube.com/watch?v=g37riSkyZzM

  9. #9
    Join Date
    Mar 2012
    Location
    Georgia
    Posts
    21
    Burnouts in Heat Pumps are very troublesome because of the possibility of getting debris in the check valves, reversing valve etc. I would encourage the customer to replace the unit before heading down the path to multiple compressor failures & big $$$$.

  10. #10
    Join Date
    Dec 2006
    Location
    new england
    Posts
    652
    I can't tell how the cage is anchored. Can it not be removed? I'd try to remove it before I had to work off of a ladder. I'm sure you already looked into this though...
    Chaos equals cash$$$

  11. #11
    Join Date
    Jan 2011
    Location
    Metro Atlanta
    Posts
    790
    The cage will be removed prior to work starts, and it's anchored in to concrete.

    I am not sure how I am going to remove it, it's a custom cage made out of rebar, and has a * pattern on top to make it impossible to service in any way.

    The unit is too tall not to work off a ladder.
    The opinions expressed by me are not that of my employer.


    insulation modern marvels
    http://www.youtube.com/watch?v=g37riSkyZzM

  12. #12
    Join Date
    Nov 2008
    Location
    baltimore
    Posts
    26
    if you put in shut off valves your clean up will be easier. When you go back to change driers.

  13. #13
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    498
    I think I would forget the Scavenger and install flare suction and liquid line filters. You could also install ball valves with access valves so you can get the pressure drops across the filters so you know when to chenge them. This will also make changing the filters quick and easy. Get the pressure when you start it up and go back in a few days and get it again. When the system is clean and no more acid detected, I would remove the suction filter and replace it with a section of pipe and install a new liquid line filter.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event