Thread: Goodman heat pump - blower motor run capacitor failed twice, what's wrong?

  1. #21
    Join Date
    Dec 2012
    Posts
    20
    Post Likes
    Thread Starter
    Ok, fun new problem. I ordered a new motor. The technician who was at my home advised me that to motor in my system was improperly sized, at 1/3 HP, and should have been a 1/2 HP. I installed the new motor, and it worked fine for about a day, and then on the next start it sounds horrible and has a noticeable vibration which you can hear through the entire house, and even see in the video below.

    Please check this video:

    http://youtu.be/7sdlgDdrqPw

    The mounting bolts are tight. The cage attachment is firm (shaft does not spin within the cage). The blower housing is attached firmly.

    Is this:

    (A) Defective motor?

    (B) Defective installation?

    (C) None of the above, just a merry Christmas gift to my sick 5 month old son.

  2. #22
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    My guess would be (B) Installation problem.

    It's time to throw in the towel. You've attempted to install it yourself and it didn't work..so call a professional. No DIY advice.

  3. #23
    Join Date
    Dec 2012
    Posts
    20
    Post Likes
    Thread Starter
    Ugh. Merry Christmas to me. I can't afford this right now. I want to throw this whole system away! Haha.

  4. #24
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Post Likes
    Jessie,

    I'm sorry to pour salt on your wounds but honestly if you had paid the tech to replace the fan motor the system would have been repaired days ago, you would not have had to worry about your wife and child being cold, and the faulty blower would be on them and not you.

    My suggestion is that you call the previous service tech and explain everything to him, be honest, be humble, and ask him for help. If money is an issue, which it is for most of us, then ask him to set up a payment plan. Offer to sign a contract for the repairs. You have options and it's best to let someone experienced handle it, and that protects your interest as well.

    If the previous tech does not want to help then look on our AOP contractors map to contact someone from the forum in your area and ask for their help. Just remember you will always catch more flies with honey than with vinegar.

  5. #25
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    Ditto on Jblack's post. Call a pro, and bite the bullet. Did ANYONE check the RPMs on old motor?? I'm assuming you got new motor over internet? They have a special "warranty" on them motors I'm sure........

  6. #26
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Quote Originally Posted by vstech View Post
    keep in mind that a few 115v "oil filled heaters" will result in an imbalanced load on the meter, causing a higher power bill than a balanced load from the 240v electric strips will.

    in the old days, each strip would have it's own fuse, and it would blow if there was too much current draw. now the entire heat strip set will be on a single breaker sized for the load, and if a single wire gets too much current, it fails. it's all in a metal box, and it's designed to fail and stay inside the box preventing a fire.
    Good points.

  7. #27
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Quote Originally Posted by Jessie james View Post
    Something has - I think - destroyed the motor run capacitor on my heat pump, but I am not sure what it is.

    Back story:

    I have a Goodman 3.5 ton heat pump, model ARUF036-00A-1A. Two nights ago I woke up to the smell of something electric burning, and the sound of the blower motor stalled while trying to start.

    The motor run capacitor is a 7.5uf and 370v, part number 27L566. I picked up a replacement capacitor, which is the same except it is rated 440v/370v at the recommendation of the local HVAC shop. This is a Mars #12931. I installed that, turned the HVAC power on, and it worked fine.

    At that time I noticed a transformer (see below, left side) in the air handler was buzzing, and I don't recall it making any noise before. I looked at it, and the fuse that is installed was not blown, so I buttoned things up.

    Last night I again woke up to the smell of something electric burning and a stalled blower motor. I turned the power off to the heat pump.

    I took photos of the heat pump innards, CLICK to get full-sized image:

    Transformer on the LEFT is buzzing:



    Motor run capacitor:



    Can someone tell me if this is a simple fix - is the transformer? Computer board? Or do I need to call someone?

    Thanks!
    Quote Originally Posted by Jessie james View Post
    Thought you'd appreciate an update - the technician diagnosed the blower motor had failed. It has ... uh ... one of the windings grounded out. Basically, it is shorting out. In addition, it spins very poorly. I've ordered a new one and will have it installed.

    He also discovered that it was the wrong sized motor. The motor is one size too small, which he says can cause premature wear because it's working too hard, and additionally it causes poor airflow. Poor airflow has been a big issue since we moved in, so hopefully the correctly sized motor will fix that, as well as better heat/cool my house.
    Why would the motor be sized wrong? I am sure you did not order the OEM replacement for the unit. Remember when trying to save money you will usually end up spending more.
    I think we let this one get to out of hand.

  8. #28
    Join Date
    Dec 2012
    Posts
    20
    Post Likes
    Thread Starter
    Quote Originally Posted by wahoo View Post
    Ditto on Jblack's post. Call a pro, and bite the bullet. Did ANYONE check the RPMs on old motor?? I'm assuming you got new motor over internet? They have a special "warranty" on them motors I'm sure........
    JD, Wahoo, you are both offering sound advice. I'm just a little put out. I do have the tech scheduled to come out and look at it. They were nice, I can't imagine they'd be rude.

    The last motor was clearly toast, it would barely spin. Yes, I ordered the new motor online here:

    Links to direct purchase sites are not permitted here.

    I just can't see how I screwed up the install. It's trivial. Unscrew the set screw from the blower fan that attached to the motor shaft. Unbolt three bolts from the old motor. Slide old motor out. Swap metal bushings from old motor mount holes to new motor mount bushings. Slide motor in. Install bolts. Be sure set screw is on flat edge of motor shaft. Install set screw on blower fan to motor shaft. Slide housing into air handler and bolt it in. Wire using existing wires which match identically. Test.

    The motor ran fine for a day, at least 10 hours of use. Suddenly on the start up yesterday afternoon it sounds like someone dropped a rock in the motor.

    Yeah, in the end I probably ruined it somehow. That's okay. At least I gave it a try. I'd rather break something and learn a lesson than not. So I'm going to be broke for a month, nothing new. That's life!
    Last edited by beenthere; 12-21-2012 at 01:14 PM. Reason: Link to direct purhcase site

  9. #29
    Join Date
    Dec 2012
    Posts
    20
    Post Likes
    Thread Starter
    Quote Originally Posted by n7943h View Post
    jessie,
    The burned wire was caused by a bad connection which caused resistance locally and high heat which melted the fitting and ends of the wire and not related to your motor issues. The new wire and good fitting connection should be the end of that problem. That loose connection did not cause increased currant flow (amps) so the breaker would not protect the wire in that case.
    Thanks for the explanation.

    Quote Originally Posted by n7943h View Post
    Can you get a view of the blower squirrel cage and watch it while it is running to see if it running true in the blower housing and not wobbling?
    Ok, I did this. It is very hard to tell if it's not centered or is loose. I grabbed the cage and tried to move it every which way and it seems as solid and as tight as can be.

    Quote Originally Posted by n7943h View Post
    Watch it when it is spooling down so you can see better. If the blower ran fine without noise the first day than something has changed since then. I would start by checking the attachment of the squirrel cage again and make sure that is not loose on the shaft and hitting the sides of the blower housing or just flexing on the shaft.
    It's not hitting the sides, it's about 3/4" away on each side. I was careful to be sure it was centered in the housing for that very reason.

    Quote Originally Posted by n7943h View Post
    I have seen the actual squirrel gage break. With the power off give everything a tug and shove. If everything looks and feels normal and it still makes that noise and vibration you can remove the assembly and dismantle it and run just the motor by itself and see if the problem goes away. Make sure that the motor shaft runs perfectly true because anything but perfect will make the cage wobble and produce vibrations at speed. I would bet it runs fine and smooth and the issue is with the cage and its mounting. Make sure nothing is inside the cage and causing it be unbalanced ( are you missing a glove?)
    I may do that. No lost gloves! Haha.

    Quote Originally Posted by n7943h View Post
    Good on ya for learning about you equipment and learning how to maintain it and I wish you a merry Christmas and a warm house.
    Thanks very much!

    Well, now get this. After I yanked and tugged and etc., the noise is gone! Somewhere a screw or a bolt is loose, and it's probably in the 6' 4" tall, 180 pound homeowner ...

    So, I'm an idiot (like someone's signature on this thread mentions) and installed it wrong somehow. I am going to let the techs come fix it proper.

  10. #30
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    The squirrel cage has balance weights on it to keep it from wobbling, its easy to knock one off or misalign one when reinstalling a motor. Also the band or ears that hold the motor in should have some type of rubber washer to prevent vibration of metal on metal.

  11. #31
    Join Date
    Dec 2012
    Posts
    20
    Post Likes
    Thread Starter
    Update: I removed the set screw from the cage/shaft, repositioned the cage slightly, tightened it back up and now the noise is gone.

    Question: There is still a small amount of vibration present. Is this normal?

  12. #32
    Join Date
    Dec 2012
    Posts
    20
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    The squirrel cage has balance weights on it to keep it from wobbling, its easy to knock one off or misalign one when reinstalling a motor. Also the band or ears that hold the motor in should have some type of rubber washer to prevent vibration of metal on metal.
    What do those weights look like? When I was taking it out, a white plastic washer (broken in half) fell out of the blower motor housing:



    The rubber grommets are in place, and the metal bushings from the old motor grommets were moved to the new motor.

  13. #33
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Strange thing though. Is you installed the wrong motor if you put a 1/2HP in.

    That tech was wrong about what size it should have.

  14. #34
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Post Likes
    You said you called the tech but you still continue to work on it and go against our advice. This is clearly too much DIY .....

    You're going to forget to pull a disconnect and wind up face down or have a blower start and Yank a finger off.

    Stop now!


    Sent from my ERIS using Tapatalk 2

  15. #35
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    That "white plastic washer piece" looks suspiciously like an insulator bushing from your heating elements. Hope it's not and I'm wrong. You might keep it and show it to your tech when he comes out.

  16. #36
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Quote Originally Posted by wahoo View Post
    That "white plastic washer piece" looks suspiciously like an insulator bushing from your heating elements. Hope it's not and I'm wrong. You might keep it and show it to your tech when he comes out.
    Is it ceramic or plastic OP? That is not a balancing weight, they are little metal clips.

  17. #37
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Quote Originally Posted by beenthere View Post
    Strange thing though. Is you installed the wrong motor if you put a 1/2HP in.

    That tech was wrong about what size it should have.
    That's the point I was trying to make but like most of my posts it was ignored. Sometimes people only hear what they want to,
    Everything else is just blabber.

  18. #38
    Join Date
    Dec 2012
    Posts
    20
    Post Likes
    Thread Starter
    Quote Originally Posted by jdblack View Post
    You said you called the tech but you still continue to work on it and go against our advice. This is clearly too much DIY .....

    You're going to forget to pull a disconnect and wind up face down or have a blower start and Yank a finger off.

    Stop now!
    Take a deep breath, it's going to be okay! I'm very competent at electrical, mechanical, and other items. I've plenty of experience around gas & electric motors, high voltages, capacitors, fan blades and the hazards of fingers and loose items of clothing. I just don't happen to understand exactly what is going on here and wanted some expert advice to round out what I already know.

    Quote Originally Posted by jtrammel View Post
    Is it ceramic or plastic OP? That is not a balancing weight, they are little metal clips.
    Ceramic.

    Quote Originally Posted by wahoo
    That "white plastic washer piece" looks suspiciously like an insulator bushing from your heating elements. Hope it's not and I'm wrong. You might keep it and show it to your tech when he comes out.
    It probably is. Time to have the heat pack checked out too.

    Quote Originally Posted by toocoolforschool View Post
    That's the point I was trying to make but like most of my posts it was ignored. Sometimes people only hear what they want to,

    Everything else is just blabber.
    I didn't mean to ignore your comment about the motor, but you didn't says what the ramifications are. Fire? Death? Destruction? Today is the end of the world after all, does it start in my utility room?

  19. #39
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    I don't want to get too negative but if you have so much experience why all the problems.
    No it dosen't start there but in your wallet and you family looking at dad like he has lost his mind.

    Ceramic.


    It probably is. Time to have the heat pack checked out too.


    I didn't mean to ignore your comment about the motor, but you didn't says what the ramifications are. Fire? Death? Destruction? Today is the end of the world after all, does it start in my utility room? [/QUOTE]

  20. #40
    Join Date
    Jan 2008
    Location
    Texas
    Posts
    7,957
    Post Likes
    I can't remember all the posts now but an off balanced blower wheel could have contributed to its failure.

Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •