Thread: Vibration form AC conducting through walls

  1. #1
    Join Date
    Dec 2012
    Posts
    5
    Post Likes

    Vibration form AC conducting through walls

    Hello. This is another question about AC on the roof of a condominium. I am on the top floor of the condo. When a single AC unit turns on, I get vibrations through the walls. The builders put spring lifters on the AC units but this didnt help. The issue is with the vibrating "tubes" from the roof units which go down through the walls. Any suggestions on how to dampen the vibrations from these as they pass through condo walls?
    Thanks so much.

  2. #2
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    What does it sound like? If the unit is low on charge it can be noisy a liquid line but I don't know about vibrations. It will be a surging sound like bubbles in the liquid line sounds like.

  3. #3
    Join Date
    Dec 2012
    Posts
    5
    Post Likes
    Thread Starter
    The sound is a low frequency hum really. It is present anytime a AC unit on the roof turns on. It is a low background noise coming through the wall from the AC cables that come from the ac fans and course down through the condo walls. These "cables" or condensers or whatever they are are wrapped but still vibrate to the touch up on the roof as they go down through the condo.

  4. #4
    Join Date
    Dec 2012
    Location
    Rancho Cucamonga, CA
    Posts
    22
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 12-14-2012 at 04:38 PM. Reason: Non Pro * Member

  5. #5
    Join Date
    Dec 2012
    Location
    Rancho Cucamonga, CA
    Posts
    22
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 12-14-2012 at 04:39 PM. Reason: Non Pro * member

  6. #6
    Join Date
    Dec 2012
    Posts
    5
    Post Likes
    Thread Starter
    Quote Originally Posted by Justhowe View Post
    The top part of my response I quoted but was unable to figure out how to link it.
    The spring mounts didnt work so far.
    The conduits going down into the building still vibrate.
    But thanks for suggestions.

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Justhowe, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Your post has been deleted.
    Further infractions may result in loss of posting privileges.

  8. #8
    Join Date
    Mar 2003
    Posts
    1,234
    Post Likes
    Contact your Carrier dealer and have him install a mass dampner as a first step and then add vibration eliminators or pipe in an inverted U in the refrig. line if the dampner doesn't resolve it. Done this numerous times with great success. Also make sure the system is properly charged like someone already mentioned.

  9. #9
    Join Date
    Dec 2012
    Posts
    5
    Post Likes
    Thread Starter
    I appreciate the professional suggestion. I am just the owner of the condo unit. If I showed that to the builder would they know what you mean? Could you put that in lay terms? Again I really appreciate it.

  10. #10
    Join Date
    Oct 2012
    Location
    Corryton,TN
    Posts
    73
    Post Likes
    I have seen this problem many times and most of the time going to the attic and simply pulling up or down on the refrigerant piping or stopped the noise. Have the unit running with someone listening to tell you when it goes away. You may have to put a hanger or something to hold them in place.I hope this helps.

  11. #11
    Join Date
    Dec 2012
    Posts
    5
    Post Likes
    Thread Starter
    Quote Originally Posted by buzhall View Post
    I have seen this problem many times and most of the time going to the attic and simply pulling up or down on the refrigerant piping or stopped the noise. Have the unit running with someone listening to tell you when it goes away. You may have to put a hanger or something to hold them in place.I hope this helps.

    thank you. The issue is this is a condo so there is no attack.
    Could someone give me a good idea of what might the builder do. they tried sprig lifters on the ac fans on the roof and that didnt work bc the things coming through the wall still vibrate andmake noise

  12. #12
    Join Date
    Jan 2008
    Location
    Texas
    Posts
    7,957
    Post Likes
    I don't know if they even still make this but 10 years I had an issue similar to that and finally ended using flexable pieces of lines that were about 10 inches in length. Thet were brazed in and insulated. Solved the problem and as far as I know is still there. They actually looked like stainless braided lines.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •