    Reznor Warehouse Furnace

    I am confused at this point ...... so I have reznor warehouse furnaces .... i can get the exact model if needed, well we went to fire them up this year and alot of them are not working so based on what i had found last year with 2 other ones, I know i have to replace the honeywell vr8305k4241 valve, so i ordered a new one and replaced it still the same thing so i came to discover that the actual regulator was bad and not letting gas through so i replaced the regulator today and still nothing, it does not seem that gas is getting pas the honeywell valve and i veried i am getting gas up to the valve, the the furnace goes through its cycle you can hear and feel the valve "turn on" but still no gas, does anyone have any suggestions? I even tried for the hell of it another valve that i had and the same thing i am stumped

    thanks

  2. #2
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    798
    Post Likes
    What was the voltage at the valve when you herd it " turn on" and what gas pressure did you set the new regulator for. If the gas pressure is too high, the valve won't open.

  3. #3
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    Could have saved some time by troubleshooting a little better!

    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  4. #4
    Join Date
    Nov 2012
    Location
    PA
    Posts
    56
    Post Likes
    Check the burner orifices to see if they are plugged. I've seen them plugged with bugs and spider webs. Also check gas pressure in and out of valve.

  5. #5
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,424
    Post Likes
    Then set the gas pressure with your manometer.... Had new Honeywell valve today that wasn't set from the factory. 0" wc

  6. #6
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    keep throwing parts at it; there aren't but ...what 6 parts total, then you'll have spares for the next go round.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  7. #7
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,186
    Post Likes
    Manual safeties, flame rod, control voltage, thermostat, gas pressure in, gas pressure out, end switch, Induced draft motor, flue, ignition control, plenty of things that can be diagnosed as good or bad. Starting off with the correct installation and operation manuals is always good. Most can be found online for free.

    ...Ron
    Roof Rat

  8. #8
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by craig wasilak View Post
    I am confused at this point ...... so I have reznor warehouse furnaces .... i can get the exact model if needed, well we went to fire them up this year and alot of them are not working so based on what i had found last year with 2 other ones, I know i have to replace the honeywell vr8305k4241 valve, so i ordered a new one and replaced it still the same thing so i came to discover that the actual regulator was bad and not letting gas through so i replaced the regulator today and still nothing, it does not seem that gas is getting pas the honeywell valve and i veried i am getting gas up to the valve, the the furnace goes through its cycle you can hear and feel the valve "turn on" but still no gas, does anyone have any suggestions? I even tried for the hell of it another valve that i had and the same thing i am stumped

    thanks
    Sounds like is time for a new unit

  9. #9
    Join Date
    May 2002
    Posts
    949
    Post Likes
    I am assuming your the property owner or his rep or employee...

    May I suggest having a competent local contractor assist you ...

    Gas is nothin' to play with or guess if it's right.....

    You should know your pressures incoming to the regulator ,after the reg,after the valve and if it's modulating high and low fire need set properly as well...amongst other things....

  10. #10
    Join Date
    Jun 2006
    Location
    midwest
    Posts
    135
    Post Likes
    Does the pilot lite? then go out. IGnition control board

  11. #11
    Join Date
    Oct 2005
    Location
    B.C. Canada
    Posts
    1,267
    Post Likes
    It probley just needs an oil change

  12. #12
    Join Date
    Aug 2006
    Location
    Colorado
    Posts
    364
    Post Likes
    I was working on some reznors with problems. I finally found out that after running for about 7-8 minutes, the pressure on the pressure switch would slowly and steadily drop until it would start cycling the pressure switch and slamming the gas valve open and closed enough that it would fail. I didn't find out till using a manometer with a tee and wondering what the H**l was going on.

  13. #13
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Really?

  14. #14
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    It's the thermostat. It's always the thermostat.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  15. #15
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,186
    Post Likes
    Quote Originally Posted by 2sac View Post
    It's the thermostat. It's always the thermostat.
    That's right blame it on the controls guy. Its always the controls guy.

    ...Ron
    Roof Rat

  16. #16
    Join Date
    Oct 2005
    Location
    B.C. Canada
    Posts
    1,267
    Post Likes
    Really! I would start with and oil change, if that doesnt work, check the cap, rotor and wires... if that doesnt do it, you might need a new transmission ($$$$$$)
    :-S

  17. #17
    Join Date
    Oct 2005
    Location
    B.C. Canada
    Posts
    1,267
    Post Likes
    Oh and we all know if none of that works, its obviously the controls guys fault! :-)

  18. #18
    Join Date
    Oct 2005
    Location
    B.C. Canada
    Posts
    1,267
    Post Likes
    Gimme another beer

  19. #19
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  20. #20
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    It helps to turn the valve "on" :beer:

    Sent from my SGH-T999 using Tapatalk 2

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •