Results 1 to 13 of 23
    Dec 2012
    Reznor Warehouse Furnace
    I am confused at this point ...... so I have reznor warehouse furnaces .... i can get the exact model if needed, well we went to fire them up this year and alot of them are not working so based on what i had found last year with 2 other ones, I know i have to replace the honeywell vr8305k4241 valve, so i ordered a new one and replaced it still the same thing so i came to discover that the actual regulator was bad and not letting gas through so i replaced the regulator today and still nothing, it does not seem that gas is getting pas the honeywell valve and i veried i am getting gas up to the valve, the the furnace goes through its cycle you can hear and feel the valve "turn on" but still no gas, does anyone have any suggestions? I even tried for the hell of it another valve that i had and the same thing i am stumped
    thanks
    Sep 2006
    Ohio
    What was the voltage at the valve when you herd it " turn on" and what gas pressure did you set the new regulator for. If the gas pressure is too high, the valve won't open.
    Feb 2007
    Fremont, Indiana
    Could have saved some time by troubleshooting a little better!
    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"
    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein
    Nov 2012
    Check the burner orifices to see if they are plugged. I've seen them plugged with bugs and spider webs. Also check gas pressure in and out of valve.
    NH
    Then set the gas pressure with your manometer.... Had new Honeywell valve today that wasn't set from the factory. 0" wc
    keep throwing parts at it; there aren't but ...what 6 parts total, then you'll have spares for the next go round.
    Jul 2003
    Orange County N.Y.
    Manual safeties, flame rod, control voltage, thermostat, gas pressure in, gas pressure out, end switch, Induced draft motor, flue, ignition control, plenty of things that can be diagnosed as good or bad. Starting off with the correct installation and operation manuals is always good. Most can be found online for free.
    ...Ron
    Roof Rat
    up in the hizzy
    Quote Originally Posted by craig wasilak View Post
    thanks
    Sounds like is time for a new unit
    May 2002
    I am assuming your the property owner or his rep or employee...
    May I suggest having a competent local contractor assist you ...
    Gas is nothin' to play with or guess if it's right.....
    You should know your pressures incoming to the regulator ,after the reg,after the valve and if it's modulating high and low fire need set properly as well...amongst other things....
    mikeacman
    Jun 2006
    midwest
    Does the pilot lite? then go out. IGnition control board
    Oct 2005
    B.C. Canada
    It probley just needs an oil change
    Colorado
    I was working on some reznors with problems. I finally found out that after running for about 7-8 minutes, the pressure on the pressure switch would slowly and steadily drop until it would start cycling the pressure switch and slamming the gas valve open and closed enough that it would fail. I didn't find out till using a manometer with a tee and wondering what the H**l was going on.
    Jul 2012
    Western KY
    Really?