    Quote Originally Posted by Healey Nut View Post
    You had better learn to develop "a feel" and quick . Not sure if you have taken the time to look but some of the flat gaskets are not really accesible with a 18" long torque wrench ,plus if you start adding extensions and wobble drives and knuckle joints your torque setting is out the window . And if you have vibration on a Trane centravac you have much bigger problems to worry about than a leaking O ring as it will becoming apart for a whole teardown .
    Healey I was just talking everyday normal vibration and ya I was trying to do some compressor bolts and the damn pipe for the econo is in the way gonna need more knuckle joints and extentions.
    ottawa canada
    Why waste your time trying to tighten compressor bolts , they dont come loose and on the newer machines theres no O ring in there anyway , all you are concerned about is the flat gasket joints.
    Dec 2012
    Well that was a waste of half of a night , but the important thing is that I learned something , I guess I need to pay better attention , point well taken .thanks for all of your post your time and expertise is muchly appreciated .
    Dec 2012
    Quote Originally Posted by klove View Post
    Metal to metal fits don't need to be retorqued to stop a leak. Economizer flange bolts I believe are 3/8" rated at 35 lbs/ft +/-. Don't crush or squeeze the gaskets out of the fit or you'll just defeat the purpose.
    Thank you Klove for replying the reason I was asking about the metal to metal seals was because the Trane Tech that worked on one of the CVHE here had cut all the insulation of around the compressor and and suction 90 degree elbow and retorqued all the bolts , I figure if he was doing it there must of been a reason , very green and trying to learn .
    Dec 2012
    Healey Nut I was asking about the metal to metal seals was because the Trane Tech that worked on one of the CVHE here had cut all the insulation off around the compressor and and suction 90 degree elbow and retorqued all the bolts , I figure if he was doing it there must of been a reason
    Foot pounds in the right arm , inch pounds on the left .
    Nice reply!!!
    Aug 2009
    Prattville, Alabama
    Which begs the question, "so, are you right-handed or left-handed?" On second thought, I don't wanna know!
    ottawa canada
    Im ambidextrous
    Aug 2009
    Prattville, Alabama
    Im ambidextrous
    Now that's funny!
    When the sealant they use on the metal to metal flanges is still wet, I apply final torque within an hour of putting the flanges together. The number is not as important as having even surface tension on the flange all the way around. All of the compressor bolts are 5/8" grade 5. The torque spec for them is 120-165 ft./lbs. The most important thing to take into consideration when you're trying to evenly torque the bolts is how clean the threads of the casting and the bolts are. If I can't easily thread every bolt into every hole by hand almost all the way with a tiny amount of never-seize on the tip, they're not clean enough, in my mind, to get a consistent torque on the flange. If the bolts give resistance, they'll make your wrench "click" prematurely. The sealant used at the factory hardens from the inside out, and once it's hard, the bolts will not come loose. If you have a leak on a compressor flange, you have to take it apart to fix it right. No shortcuts, unfortunately. One thing I can tell you is don't put 30-35# on the econo bolts. In my experience, the 14-16# factory spec can even be too much. I've gotten used to going by feel and sight on rubber gaskets. If the gasket is pushing out of the flange, it's too tight.
    Dec 2012
    Thank for the great info Rob , I appreciate your time and expertise , cheers!!
    I appreciate your time and expertise for any of the question I ask
    Living the dream!!!!!!
    A recent conversation between myself and one of my colleagues went like this:
    "How do know what an inch is? How can you precisely measure it?"
    "I don't know, with a micrometer?"
    "No, just look down when you pee"
    "I'd have to look down and then divide by 12"
    No problem, Troy!