Page 1 of 3 123 LastLast
Results 1 to 13 of 28
  1. #1
    Join Date
    Dec 2012
    Location
    Hamilton Ontario Canada
    Posts
    103
    Post Likes

    Have a leaker CVHE ,

    Have a leak on one of the chillers ,I know how to heat pack and find leaks but do you guys ever go around your chiller and torque all you bolts down as like a yearly inspection type thing and if you do does anyone have the torque Specs. Cant find it anywhere in my O&M manual.

    thanks in advance

  2. #2
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,957
    Post Likes
    Yes , they should be checked once a year , as for torque specs . My torque wrench is built into my right forearm . use your common sense and dont try to get 130 ft lbs on a 5/16 bolt and you will be fine . Tight is tight , to tight is broke .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  3. #3
    Join Date
    Dec 2012
    Location
    Hamilton Ontario Canada
    Posts
    103
    Post Likes
    Thread Starter
    Thanks Healey Nut , I dont know if I have the feel and dont wanna be the guy that snapped the econimizer bolt off , there has to be some sort of bolt to torque ratio.I would feel better knowing that I followed the specs and if something goes wrong at least I can say I followed the Trane specs.

  4. #4
    Join Date
    Dec 2012
    Location
    Hamilton Ontario Canada
    Posts
    103
    Post Likes
    Thread Starter
    found this online


    Recommended Torque
    Grade 2 Grade 5 Grade 8 18-8 S/S Bronze Brass
    Coarse Fine Coarse Fine Coarse Fine Coarse Fine Coarse Fine Coarse Fine
    #4* - - - - - - 5.2 - 4.8 - 4.3 -
    #6* - - - - - - 9.6 - 8.9 - 7.9 -
    #8* - - - - - - 19.8 - 18.4 - 16.2 -
    #10* - - - - - - 22.8 31.7 21.2 29.3 18.6 25.9
    1/4 4 4.7 6.3 7.3 9 10 6.3 7.8 5.7 7.3 5.1 6.4
    5/16 8 9 13 14 18 20 11 11.8 10.3 10.9 8.9 9.7
    3/8 15 17 23 26 33 37 20 22 18 20 16 18
    7/16 24 27 37 41 52 58 31 33 29 31 26 27
    1/2 37 41 57 64 80 90 43 45 40 42 35 37
    9/16 53 59 82 91 115 129 57 63 53 58 47 51
    5/8 73 83 112 128 159 180 93 104 86 96 76 85
    3/4 125 138 200 223 282 315 128 124 104 102 118 115
    7/8 129 144 322 355 454 501 194 193 178 178 159 158
    1† 188 210 483 541 682 764 287 289 265 240 235 212
    * Sizes from 4 to 10 are in lb-in.
    Sizes from 1/4 up are in lb-ft.

  5. #5
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,228
    Post Likes
    On flanges with gaskets I tighten the bolts until I see the gasket just start to squeeze out, then I give it about another half turn. On R11 machines I stop when the gaskets begin to squeeze out (R11 gaskets are softer). Then during the leak test, if it leaks I tighten a little more until it stops leaking. I rarely, if ever have to tighten it that second time. I do this because it's possible to distort some of those gaskets.

  6. #6
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,623
    Post Likes
    Metal to metal fits don't need to be retorqued to stop a leak. Economizer flange bolts I believe are 3/8" rated at 35 lbs/ft +/-. Don't crush or squeeze the gaskets out of the fit or you'll just defeat the purpose.

  7. #7
    Join Date
    Dec 2012
    Location
    Hamilton Ontario Canada
    Posts
    103
    Post Likes
    Thread Starter
    Guys do the metal to metal fits come loose from vibration , is it a good idea to go over the chiller before you heat pack it.

  8. #8
    Join Date
    Dec 2012
    Location
    Hamilton Ontario Canada
    Posts
    103
    Post Likes
    Thread Starter
    So Klove if theres a leak on the Trane o-ring you just have to replace it , do the bolts come loose from vibration and then you dont have metal to metal contact is that possible .

  9. #9
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,150
    Post Likes
    Quote Originally Posted by Healey Nut View Post
    ...My torque wrench is built into my right forearm....
    i'm glad i'm not your weiner!
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  10. #10
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,957
    Post Likes
    Quote Originally Posted by Troy Love View Post
    Thanks Healey Nut , I dont know if I have the feel and dont wanna be the guy that snapped the econimizer bolt off , there has to be some sort of bolt to torque ratio.I would feel better knowing that I followed the specs and if something goes wrong at least I can say I followed the Trane specs.
    You had better learn to develop "a feel" and quick . Not sure if you have taken the time to look but some of the flat gaskets are not really accesible with a 18" long torque wrench ,plus if you start adding extensions and wobble drives and knuckle joints your torque setting is out the window . And if you have vibration on a Trane centravac you have much bigger problems to worry about than a leaking O ring as it will becoming apart for a whole teardown .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  11. #11
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,957
    Post Likes
    Quote Originally Posted by jayguy View Post
    i'm glad i'm not your weiner!
    Foot pounds in the right arm , inch pounds on the left .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  12. #12
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    348
    Post Likes
    Quote Originally Posted by Troy Love View Post
    Have a leak on one of the chillers ,I know how to heat pack and find leaks but do you guys ever go around your chiller and torque all you bolts down as like a yearly inspection type thing and if you do does anyone have the torque Specs. Cant find it anywhere in my O&M manual.

    thanks in advance
    Attached might help for reference factory flat gasket re-torque specsCTV-SVB17B-en_Torquing of Flat Gaskets.pdf
    Necessity is the mother of invention

  13. #13
    Join Date
    Dec 2012
    Location
    Hamilton Ontario Canada
    Posts
    103
    Post Likes
    Thread Starter
    Thanks Screwit

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.