Thread: mcquaid heat pump trouble
-
12-12-2012, 10:19 PM #1
Regular Guest
- Join Date
- Jun 2006
- Posts
- 12
mcquaid heat pump trouble
Got called to no heat. upon arival the heat pump was tripped on high head pressure. first i noticed that the fan was burned out and replaced that. still tripped out if reset within minutes. I replaced my filters, coils are clean and have water flow (water supplied heat pump). i know my water temp is 78 degrees. what is happeneing is that the high side runs 400 psi+ if i let it run and low side runs from 70-80 psi. i pulled my charge and recharged to factory charge. the only thing I can think of is a restriction in the system most likely in the cap tubes. Just wondering if im missing anything.
-
12-12-2012, 10:40 PM #2
Mcquaid?
Like chuck noris in
Lonewolfe mcquaid?
-
12-12-2012, 10:42 PM #3
Regular Guest
- Join Date
- Jun 2006
- Posts
- 12
mcquay woops
-
12-12-2012, 10:45 PM #4
Lol!!!
-
12-12-2012, 10:48 PM #5
If you have 78* water and 400 psi?
Your approach is too high.
Fouled tubes.
Does not sound like your heat xchanger is xchanging much heat.
-
12-12-2012, 10:50 PM #6
Regular Guest
- Join Date
- Jun 2006
- Posts
- 12
i have 78 inlet it drops 5-8 degrees outlet in heat mode for the couple minutes it runs
-
12-12-2012, 10:51 PM #7
It drops???
-
12-12-2012, 10:52 PM #8
The condenser should be giving up heat!!!
-
12-12-2012, 10:53 PM #9
Regular Guest
- Join Date
- Jun 2006
- Posts
- 12
yup
-
12-12-2012, 10:53 PM #10
Leaving water should be close to sct!
Satuated condnser temperature.
-
12-12-2012, 10:53 PM #11
Regular Guest
- Join Date
- Jun 2006
- Posts
- 12
this is when its running in heat mode
-
12-12-2012, 10:54 PM #12
Is it 410a....Is the return ducted? possible restriction on air side??? Fan going the right way. what was pressures after you recharged it
-
12-12-2012, 10:56 PM #13