Results 1 to 10 of 10
Thread: Carrier RTU-Open Problem
-
12-12-2012, 09:10 PM #1
Professional Member
- Join Date
- Dec 2006
- Location
- Boston area
- Posts
- 159
Carrier RTU-Open Problem
Just installed 45 new RTU's that have factory install RTU_Open controllers in them. The issue I have is on some units the unit will go into Economizer Cooling mode even though the Space temp is 5 degrees below the cooling set point. I have to raise up the cooling set point 5 degrees above space temp to get it to come out of Economizer Cooling mode. When I try to open the control program in either Application Builder or SNAP it says that program was not made with either application. Have had my Carrier controls support guy looking into it, he has seen the same problem on other RTU's, but thought I'd see if anyone else has ran into this.
-
01-05-2013, 10:05 PM #2
Which version module driver did your RTU's have in them? ( you can do a modstat and post the screen capture here)
The program for the RTU's can not be opened or edited with i-Vu SNAP, as it is locked from field editing due to warranty and liability issues related to the "factory provided controls" sequences of operations. I work with configuring and troubleshooting RTU opens almost every day, and have not seen this issue yet. Do you have the configuration manual or training Power point for the RTU Opens?
Chances are there is a Configuration setting that may need adjustment.
Respectfully
Drac
Can you post a printout of your BACnet Points tab (use the report feature)"We are what we repeatedly do. Excellence, then, is not an act, but a habit" Aristotle
Remember to "Pay it Forward"; help out the newer generation of techs, remember someone during our career helped us! ("Pay it Forward" was by someone smarter than me!!)
-
01-06-2013, 09:22 AM #3
Professional Member
- Join Date
- Dec 2006
- Location
- Boston area
- Posts
- 159
Driver Version - drv_rtuopen_std_3-04-361#discovered
Control Program - rtu_open-2_20120123
This is info from database. I am not on-line with device. I think I attached point report, but again I'm not on-line with device.
This issue is happening to a number of units. I have carrier controls tech. coming to site this week.
It does suck that you can.t view control program in either SNAP or App. Builder
-
01-09-2013, 08:18 PM #4
Professional Member
- Join Date
- Dec 2006
- Location
- Boston area
- Posts
- 159
Found out today that the way the economizer is set up in the RTU Open is that it tries to maintain a mid-point between Heat and Cool set points, if your Cool setpoint is 72 and your heat setpoint is 68 the economizer is looking to maintain 70. Doesn't make sense to me or my customer.
-
01-09-2013, 08:57 PM #5
Mechmike2,
If you want you can send me the .clipping or the program and driver and I can see if I can open it and see what is going on, maybe even modify it. I have been lucky so far, as I have been able to open some OEMCtrl clippings here lately."If you can't explain it simply, you don't understand it well enough”
Albert Einstein
"Don't you just love when the flames burn off the wiring schematic?" hvacvegas-HTALK member
-
01-09-2013, 11:09 PM #6
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,510
-
01-09-2013, 11:37 PM #7
Yea luck as in "opening" the program. I gave a copy of that program to our engineer, and for three (on and off) days he looked at that program and finally gave up on it. His comment was he thinks the programmer lives in a state that has legal marijuana.
"If you can't explain it simply, you don't understand it well enough”
Albert Einstein
"Don't you just love when the flames burn off the wiring schematic?" hvacvegas-HTALK member
-
01-09-2013, 11:38 PM #8
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,510
-
01-10-2013, 07:18 PM #9
Professional Member
- Join Date
- Dec 2006
- Location
- Boston area
- Posts
- 159
The units in question are all brand new and I wouldn't want to run into warranty issues. I am not sure what I would send you anyhow.
-
01-10-2013, 07:19 PM #10
Professional Member
- Join Date
- Dec 2006
- Location
- Boston area
- Posts
- 159
Thanks though.


Reply With Quote