Rheem heat pump
hello all
i am tkjimmy and read about this site on the reefer tech forum.
i help others every day on that site . I have 30 years in the transport refrig. business.
today i have a problem that i was hoping one of you guys could help me with.
i have a rheem RHSL-HM3617JA system and the condensing unit will not run in the heat mode,only runs on back-up heat.
it will run in the cool mode
inside the unit i see 2 led light
led1 off
led2 blinking
could someone help me with these codes please?
thanks tkjimmy
-
12-12-2012, 04:21 PM #2
Moved to tech to tech forum.
-
12-12-2012, 04:31 PM #3
You say the outdoor unit will run in Emergency Heat Mode when you set the t Stat to Emergency Heat? Emergency Heat should turn on Heat Strips on the indoor unit and the fan, that's all. It sounds like either a T Stat problem, because RHEEM requires 24 volts to reversing valve to switch to heat. In cool there will be no voltage to the reversing valve. It could also be a bad defrost board.
-
12-12-2012, 04:41 PM #4
Professional Member
- Join Date
- Nov 2012
- Location
- PA
- Posts
- 46
Could be outdoor t'stat issue as well.
-
12-12-2012, 05:10 PM #5
You gave us the model number for the air handler and not the Heat Pump (outside unit).
Those two LED's you are talking about are on the defrost control board of the Heat Pump - correct?
I think that LED combination means - LOW PRESSURE LOCKOUT
Post the model number of the outside unit for further verification.Instead of learning the tricks of the trade, learn the trade.
-
12-13-2012, 08:14 AM #6
New Guest
- Join Date
- Dec 2012
- Posts
- 2
13pjl36a01 sorry for the error.
the condensing unit does not come on in the heat mode but does in cool
-
12-13-2012, 05:18 PM #7
Sounds like a stat problem or setting.
-
12-13-2012, 07:45 PM #8
It is the same code for the 13JPL.
The compressor and fan motor will stop when the low pressure control opens, and will start again when the low side pressure rises to approximately 40 psig when the low pressure control automatically resets. If the low pressure switch trips 3 times within 120 minutes of operation during a particular call for heating operation, the defrost control will lock out compressor and outdoor fan operation.Instead of learning the tricks of the trade, learn the trade.