    Ok. This thread has me all messed up. The OP hasn't communicated the issue well. It first sounded like a RV issue now it's sounds like a control wiring issue.

    To the OP, HVAC 101. Check all the basics. Test low voltage. Confirm low voltage in correct areas. Confirm high voltage in correct areas. Ohm out all pressure switches and sensors. Connect your gauges when you first arrive and don't take them off the system until your finished.

    Once you do this, coupled with advice already given; The problem should become pretty apparent.

  2. #22
    Join Date
    Nov 2011
    Location
    Gerald, MO
    Posts
    67
    Post Likes
    Thread Starter
    Just to let you all know I did all the checks and balances and it wound up being the circuit board. I guess it was intermitent and screwed the pooch when it decided it wanted to. HO is pleased because it was under warranty, I am pleased because it is over. I have little expeirience with circuit boards and some of us are still learning. So for those of you that want to act like they know it all, you dont and nobody does!

  3. #23
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    Jeffrey,

    Great to hear that you found the problem!

    Learning. That's what this site is for. I learn something new on here almost daily. Example: Rundawg schooled me on a timed defrost issue just a few days ago.

    From what I read, I don't think anyone was acting as if they "know it all" and I certainly hope that I wasn't the one who came off like this.

    We are just a group of guys who are passionate about HVAC and volunteer their time in an attempt to help out/receive help from others. We can only help others if the correct information is relied to us. I hope you didn't get discouraged by my comments or someone else's because we need guys like you around here!

    Good luck!

  4. #24
    Join Date
    Mar 2001
    Location
    Ilwaco, Washington
    Posts
    1,638
    Post Likes
    I suspected the internal time delay on the board, but you need to verify power coming to the board thru the Y wire, and then verify the Y power leaving the board and going thru the pressure switches to the contacter. That would have showed the problem was the board. As you work with these units, it will come easier. Just working on a few of them over time will make you feel less intimidated. Take the time (when you have it) to play with a few things in the controls, and see how they react. At the very most, you may blow a control fuse, but you'll gain an understanding of what the different components do, and how the equipment acts when they don't do what they're supposed to. Make sense???
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

  5. #25
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by jeffrey43 View Post
    Just to let you all know I did all the checks and balances and it wound up being the circuit board. I guess it was intermitent and screwed the pooch when it decided it wanted to. HO is pleased because it was under warranty, I am pleased because it is over. I have little expeirience with circuit boards and some of us are still learning. So for those of you that want to act like they know it all, you dont and nobody does!
    I'm sorry, I must have missed a post where someone was "acting like they know it all."

    1) keep learning

    2) improve your attitude
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  6. #26
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by jeffrey43 View Post
    Its a GSZ1302416A Goodman Heat Pump I installed on Augest 29th of this year. The HO has been running this thing in heat mode only for the last 2 and a half months. They call last week and say its not working.
    Okay. So this is a residential install.

    Riddle me this, Batman.

    Why is this post in the Tech to Tech COMMERCIAL forum???
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  7. #27
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    798
    Post Likes
    Quote Originally Posted by jeffrey43 View Post
    Contactor pulls in compressor kicks on for a second fan does not come on at all then it all shuts down.
    I wouldn't think the board was the problem if the contactor was pulled in and the fan and compressor were not running. Sounds like the capactor might be going bad.

  8. #28
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by hands View Post
    I wouldn't think the board was the problem if the contactor was pulled in and the fan and compressor were not running. Sounds like the capactor might be going bad.
    Sounds like he needs to sit down with his boss and go over diagnostic skills.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  9. #29
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Hahahaha...This thread just keeps getting better.

    With how the OP described the problem I would never have been able to diagnose it.

    A reversing valve needs a differential pressure to shift. If you can't make this happen it won't shift.

    Glad you figured it out.

    Also, hope it's not low on charge when it's time for cooling.

  10. #30
    Join Date
    Nov 2012
    Location
    Georgia
    Posts
    13
    Post Likes
    When you say the compressor starts for a second then shuts down, I am assuming the contactor is not opening and the compressor is going out on thermal. This combined with the info that you are checking the charge in cooling mode and the only value we know is 8 degrees subcooling makes me wonder if the system may not be charged correctly.

    You stated there is no TXV so when you are checking pressures in cooling mode we need to know superheat, however, the more accurate method to check the charge would be to look at the manufacturer winter charging chart which should be with the unit unless the installer didn't leave it there.

    I have seen reversing valves shift with no noise, and, keep in mind refrigerant flow is what causes it to shift, so the unit must be running for the shift to take place.

    If the compressor is out on thermal it may take several hours to cool enough to start

    Good luck

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •