    HO called again said heat pump doing same thing again. I go and check hps ok lps ok. run it in cooling mode and unhook orange reversing valve wire and there is no swoosh. shut it off and try to let pressures equalize to no success. 120 high side 145low side. try to get it to run in ac again and it wont, wont run in either heating mode or cooling mode now. So I am thinking I am a dumb ass. Can anyone help me out.

    Thanks

    This is a continuation of an earlier post called Heat pump confusion

  2. #2
    Join Date
    Aug 2012
    Posts
    3,948
    Post Likes
    By dosen't run do you mean nothing at all or maybe indoor blower or condensing fan etc.
    Is it timing out? Can you operate the rv at all? If there is a check vlv it will not equalize. Need more info.

  3. #3
    Join Date
    Mar 2012
    Location
    West Chester, PA
    Posts
    530
    Post Likes
    If the unit is using a non bleed TXV, the pressure will not equalized (unless you let them through your manifold) don;t know what not running means.... compressor won't start or the board is holding it off?

  4. #4
    Join Date
    Nov 2011
    Location
    Gerald, MO
    Posts
    67
    Post Likes
    Thread Starter
    when in heat mode the compressor kicks on for a second and kicks back off, cooling mode wont do anything now. Last week we were having the same problem exept it would run in cooling and found it was over charged. Recovered refrigerant and got it down to manufacturer specs and then it would run in heat mode. Now this crap this week was doing same as last week, execpt when in cooling mode this week, when I disconnected the orange 4way valve wire it did not swoosh at all, then would not run after that. I am at a loss and dont know what to tell HO

    Oh one other thing no TXV its fixed orifice

  5. #5
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,937
    Post Likes
    Sounds like a reversing valve not swapping over or a possible compressor issue.

    My bet would be on the reversing valve. The article below will give you tips on troubleshooting this issue.

    Read this article by ACR News.
    http://www.achrnews.com/articles/don...e-outsmart-you

  6. #6
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    1,847
    Post Likes
    Does the contactor drop out or does the compressor shut off on overload? Did you overheat the compressor by short cycling it? 145 over 120 should not be an issue to get the compressor to start unless you have bad start components. Your gauges could even be that far out of calibration. What were the pressures in cooling mode before you pulled the reversing valve wire?
    " when I disconnected the orange 4way valve wire it did not swoosh at all, then would not run after that" Did you shut off the unit at that point or did it shut off by some other means like safeties?

  7. #7
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    29,237
    Post Likes
    This is a so called "teachable moment" for many young techs.

    Some snicker under their breath when I harp on communication skills, but those skills are KEY when describing a sequence of events for a customer, a service manager, or a bunch of strangers on an HVAC site.

    You need to be able to describe all of the steps, actions, observations, and your reactions, IN ORDER, so we can follow the events and your thinking, in order to find what you may have overlooked, and to help you understand what is actually going on.

    I want to know things like amp draw on startup. What kind of start components? For those of us who did not read the other thread: model and serial??

    Information is everything in diagnostics.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #8
    Join Date
    Nov 2011
    Location
    Gerald, MO
    Posts
    67
    Post Likes
    Thread Starter
    Its a GSZ1302416A Goodman Heat Pump I installed on Augest 29th of this year. The HO has been running this thing in heat mode only for the last 2 and a half months. They call last week and say its not working. I go and find that the compressor starts for a quick second then shuts down. I then put it in cooling mode and while its running I remove orange wire from circuit board and 4 way valve disengages so I determine the valve and solenoid are good. I block up the condensor in cooling mode to simulate a 90 degree day it was 58 degrees that day and check the charge I determine its over charged and no I dont remember the values except I had it condensing at 120 degrees and I had a subcooling of about 20 degrees, I removed 1/2 a pound of refrigerant R-410A. It was then condensing at 110 with a subcooling at about 8 degrees I think. I shut the unit off and let the pressures egualize. I turn it to heat mode and it starts right up after time delay. I let it run for 15 min. shut it off and restart it 4 times. It was working good and heating the home good as well.

    Then they call today same problem but the outside ambient was at least 15 deg colder. I fire it up in cooling mode again and go to check the 4way valve again pull orange wire and nothing, does not disengage just clicked. I wait 10 min for it to come back on and it wont ???? Now I am feeling really stupid and tell HO have to call tech support. I am going back tomorrow or actually today to see if I can get this damb thing to run. I installed 4 of these this year and all the others are doing fine I have got to be missing something or this thing is just possessed. I am learning that I need to start writting everything down.

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    29,237
    Post Likes
    Quote Originally Posted by jeffrey43 View Post
    Its a GSZ1302416A Goodman Heat Pump I installed on Augest 29th of this year. The HO has been running this thing in heat mode only for the last 2 and a half months. They call last week and say its not working.
    Okay. So this is a residential install.

    Riddle me this, Batman.

    Why is this post in the Tech to Tech COMMERCIAL forum???
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #10
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,244
    Post Likes
    You tap on the valve to make if shift?

  11. #11
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,539
    Post Likes
    Quote Originally Posted by jeffrey43 View Post
    HO called again said heat pump doing same thing again. I go and check hps ok lps ok. run it in cooling mode and unhook orange reversing valve wire and there is no swoosh. shut it off and try to let pressures equalize to no success. 120 high side 145low side. try to get it to run in ac again and it wont, wont run in either heating mode or cooling mode now. So I am thinking I am a dumb ass. Can anyone help me out.

    Thanks

    This is a continuation of an earlier post called Heat pump confusion
    Suction is higher than discharge?

  12. #12
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,539
    Post Likes
    Quote Originally Posted by jeffrey43 View Post
    when in heat mode the compressor kicks on for a second and kicks back off, cooling mode wont do anything now. Last week we were having the same problem exept it would run in cooling and found it was over charged. Recovered refrigerant and got it down to manufacturer specs and then it would run in heat mode. Now this crap this week was doing same as last week, execpt when in cooling mode this week, when I disconnected the orange 4way valve wire it did not swoosh at all, then would not run after that. I am at a loss and dont know what to tell HO

    Oh one other thing no TXV its fixed orifice
    If it is overamping or opening internal overload, it may have washed the oil out of the compressor from previous overcharge.

  13. #13
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,702
    Post Likes
    Quote Originally Posted by timebuilder View Post
    This is a so called "teachable moment" for many young techs.

    Some snicker under their breath when I harp on communication skills, but those skills are KEY when describing a sequence of events for a customer, a service manager, or a bunch of strangers on an HVAC site.

    You need to be able to describe all of the steps, actions, observations, and your reactions, IN ORDER, so we can follow the events and your thinking, in order to find what you may have overlooked, and to help you understand what is actually going on.

    I want to know things like amp draw on startup. What kind of start components? For those of us who did not read the other thread: model and serial??

    Information is everything in diagnostics.

    PREACH, BROTHER!




    Quote Originally Posted by SBKold View Post
    You tap on the valve to make if shift?
    Don't tell'em to do that unless your confident they are capable.
    It`s better to be silent and thought the fool; than speak and remove all doubt.