Results 1 to 13 of 34
    mcquaid heat pump trouble
    Got called to no heat. upon arival the heat pump was tripped on high head pressure. first i noticed that the fan was burned out and replaced that. still tripped out if reset within minutes. I replaced my filters, coils are clean and have water flow (water supplied heat pump). i know my water temp is 78 degrees. what is happeneing is that the high side runs 400 psi+ if i let it run and low side runs from 70-80 psi. i pulled my charge and recharged to factory charge. the only thing I can think of is a restriction in the system most likely in the cap tubes. Just wondering if im missing anything.
    8th grade
    Mcquaid?
    Like chuck noris in
    Lonewolfe mcquaid?
    mcquay woops
    8th grade
    Lol!!!
    8th grade
    If you have 78* water and 400 psi?
    Your approach is too high.
    Fouled tubes.
    Does not sound like your heat xchanger is xchanging much heat.
    i have 78 inlet it drops 5-8 degrees outlet in heat mode for the couple minutes it runs
    8th grade
    It drops???
    8th grade
    The condenser should be giving up heat!!!
    yup
    8th grade
    Leaving water should be close to sct!
    Satuated condnser temperature.
    this is when its running in heat mode
    Oct 2005
    Is it 410a....Is the return ducted? possible restriction on air side??? Fan going the right way. what was pressures after you recharged it
    8th grade
    Sorry!
    I am always stuck in cooling!!!!!
    Lol
    Quote Originally Posted by hvac_man17 View Post