    Is it alright to run a Goodman ARUF303016 air handler with 10kW of heat that has lost it's heat pump? It will be some time before the hp is on line and it is cold in here.

  2. #2
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,403
    Thats the beauty of a heat pump with electric strips for back up... switch the stat over to emergency heat and get warm!
    "If you call that hard work, a koala’s life would look heroic."

    VETO PRO PAC, The Official Tool Bag of HVAC-Talk.com

    Testo... you guys rule!

  3. #3

    Thanks

    Thanks.

  4. #4
    Join Date
    Oct 2003
    Location
    Washington
    Posts
    7,405
    Just don't do it for a prolonged time, you won't like your electric bill!

  5. #5
    Join Date
    Apr 2004
    Posts
    7,680
    just make sure you switch the stat to emergency heat, not just run it as aux heat. That way the stat operates the heat at the set point, not 2 degess lower.