    Auxiliary Heat running too much

    I have an Amana heat pump and air handler with a Honeywell Prestige thermostat which was all newly installed this past July. I have noticed that the Auxiliary heat is probably on about 15 minutes per hour. The house temp is set at 68 and the outdoor temp has been in mid forty to mid 50 range. Even when temp in house is at 68 the auxiliary heat comes on. My last months electric bill was through the roof and I think it is because aux heat was on so much. The company who installed it is coming out tomorrow to look but they were out a month ago and said everything was fine. Clearly something is wrong. Is there a temperature setting that triggers when aux heat comes on that is maybe set too high?

  2. #2
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    1,928
    You have a couple of isssues that could be possible.
    1. Heat Pump could be to small, although this is fairly rare
    2. Heat Pump not installed properly
    3. Thermostat not setup properly for staging of heat pump and auxillary heat
    4. No outdoor temperature sensor on thermostat to lock out auxillary heat. On all of our systems we lock out auxillary heat strips unless the temperature is below 30 or 35 depending on the situation.
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  3. #3
    Thanks Sky - there is an outside temp that shows on thermostat but I am thinking that when the unit was set up I don't think they locked out until a lower temp was reached (i.e. the 30/35 you mentioned). Does that sound like a possible root cause? They will be out tomorrow and I wanted to have some knowledge on this in case they tell me everything looks good again.

  4. #4
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,119
    I staged my heat strips to use 1/2 in emergency mode.
    you may want to ask about that.
    been watching my utility bill like a hawk..$43 this month
    for 377Kwh

    good advice from sky.

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,595
    Probably didn't set a lock out temp. but something else is still wrong if it needs to bring on the aux heat when its that warm out just to maintain temp.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event