12-13-2012, 08:01 AM #14
Regular Guest
- Join Date
- Dec 2012
- Posts
- 21
With the water supply valve open all of the way, the Flow Rate on the Water meter reads ".000" I found out that the leak showing up on the meter was from the basement toilet reservoir.
How hard should I tap it? With the water supply valve open, there is no change in pressure.
The furnace is currently off and showing 0 psi at 120f.
When the furnace is turned on, the Taco pump sounds like this -
-
12-13-2012, 09:28 AM #15
Regular Guest
- Join Date
- Dec 2012
- Posts
- 21
The expansion tank is this one http://ecomfort.com/fill-trol-110-ex...10-1-3093.html . When I measure the tank it reads at less than 5 psi, when I first checked it - a small amount water came out. Is that normal after 5 years?
-
12-13-2012, 10:08 AM #16
I didn't watch the video but read enuf to know that you need a good boiler guy, it is common for a water feed to stick shut and also the exp tank can loose pressure, on an annual service they should check all of that. If you keep running it with no pressure you will burn out the pump. There also must be a leak In the system for the pressure to drop.
-
12-13-2012, 10:38 AM #17
Regular Guest
- Join Date
- Dec 2012
- Posts
- 21
-
12-13-2012, 12:58 PM #18
Regular Guest
- Join Date
- Dec 2012
- Posts
- 21
i recharged the expansion tank to 12psi, no change in the boiler pressure meter, its still at 0psi. Still no water flow from the supply line either.. im guessing its stuck closed as suggested, i tapped it with a wrench and no change either.
-
12-13-2012, 01:56 PM #19
first off the safty relief must be changed to a 30# the auto fill is actually a pressure reducing valve which constantly maintains pressure to the boiler (though not if supply is off ) they have a screen under a nut on the bottom should be cleaned the reducing valve should be factory set @ 12 # which is 40% of relief which is normal pressure cold / standing. these issues must be addressed the relief valve is for demestic water heater and is not safe !!!!!!!!!!!! firing your boiler dry it could explode expecially with that relief valve
-
12-13-2012, 04:19 PM #20
Regular Guest
- Join Date
- Dec 2012
- Posts
- 21
Anyone have a clue on how much this might all cost? :-/ I suspect a lot..
-
12-13-2012, 05:10 PM #21
I didn't realize you had that style fill valve, they aren't to costly, I see them fail a lot. It's hard to guess what other service company's will charge but opening a boiler system can turn into a project depending on how much air you have to purge out. I know about how much I would charge but we aren't allowd to talk about pricing anyways. If this makes no sense most of my screen is cracked so I can't tell exactly how this is going lol.
-
12-13-2012, 05:18 PM #22
Regular Guest
- Join Date
- Dec 2012
- Posts
- 21
It's okay lol, I've worked on computers for the last 10 years and those are kind of my specialty. I like to work on tips - I know everyone can't afford it.
It does make sense though about the pricing. From what I can tell though, the parts alone are at a minimum going to run about $, maybe $. Are parts pricing anything you can comment on? Or maybe just a parts list?Last edited by beenthere; 12-13-2012 at 05:34 PM. Reason: price range
-
12-13-2012, 05:35 PM #23
No prices are allowed.
-
12-13-2012, 06:06 PM #24
Regular Guest
- Join Date
- Dec 2012
- Posts
- 21
-
12-13-2012, 06:48 PM #25
Regular Guest
- Join Date
- Dec 2012
- Posts
- 21
So From what I can tell, about 6 parts need to be replaced. 2 auto-air purgers (I found one that was corroded in the upstairs radiator that had the cap on so tight i had to use pliers to take it off, a No.67), a motor cartridge for the taco, an auto-fill pressure relief valve, a water supply valve, and a pressure relief valve.
Also, I was informed that the drain faucet at the bottom of the boiler has been leaking for the last 2 years - smalls drops.
-
12-13-2012, 07:09 PM #26
The auto fill and pressure reducing valve are the same, the boiler drain just needs a hose cap, the auto vents can be cleaned and I don't like to change them because I don't leave them open once the air is out. I didn't see all the vid but the pump is bad?