Results 1 to 2 of 2
  1. #1
    Join Date
    Apr 2012
    Location
    Princeton NJ
    Posts
    125
    Post Likes

    Variable speed furnace amps?

    Hi,
    Can i bother someone to explain what is the amp rating of my trane xv95 120btu furnace----the plate inside says "15 amps", I am comparing this to an old single speed 80 btu trane xe90 i have---and it says "10 amps". Proportionally that is the same electric motor efficiency. I was lead to believe that the variable speed motor is 70% more efficient--I was expecting the amp rating to be about 5 rather than 15.

    Thanks (I"m having a whole house/part house generator installed and was told to gather this for unit sizing).

    Steve

  2. #2
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    3,113
    Post Likes
    Your ductwork design will make a big difference in the amp draw of the motor. Smaller ducts cause higher amp draw as it takes energy to overcome resistance. On a 120k unit most homes will have inadequate duct sizing. Your "70%" savings in electrical is based on continuous fan operation as the variable speed motor will run much lower cfm at that speed as compared to a multi speed motor. Without putting an amp probe in your motor we would be guessing. I would play it safe and assume 1800 watts. If you are using a load shed panel for your generator it should not be a major issue.
    ...

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.