    Confused Have to change oil on low pressure Chillers and have never done it before

    Hey guys have I am a 5th year apprentice and given the job of changing the oil on 4 CVHF 700 tonners and 2 2550 CDHF dualees , have done the purge filters and and oil filters but not sure on how to do the oil , Im a visual person and reading the operation and maintenance manual dosent tell me very much besides do it though the oil charging valve , I know this is simple for you guys but I'm just looking for some direction so that I dont get air into the chiller.

  2. #2
    Join Date
    Mar 2007
    Posts
    3,108
    Moderators, please move this thread to one of the chiller forums.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,095
    Moved to chiller forum.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    There are a couple of different ways to perform the maintenance procedure,

    Get pro status and you may get the info You are looking for.
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  5. #5
    Join Date
    Jan 2011
    Posts
    1,170
    Quote Originally Posted by milkyway View Post
    There are a couple of different ways to perform the maintenance procedure,

    Get pro status and you may get the info You are looking for.
    This isn't rocket science. Do you perform annual service on these chillers? How do you leak check them? That should give you one method. If you use hot water to heat the machines then you can get the oil out when the machine is under positive pressure.

    Another method is an electric oil pump. Far easier and quicker than pressurizing the machine. Hook the suction side of the pump to the oil charging valve, start the pump and slowly open the charging valve. Make sure the discharge hose is secured in an empty bucket. Stop/repeat as necessary to get all the oil out. Make sure you don't turn off the pump before closing the charging valve.

  6. #6
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    Yep, that is what I was going to suggest.
    1.Pressurize
    2.Pump

  7. #7
    Join Date
    Dec 2012
    Location
    Hamilton Ontario Canada
    Posts
    103
    Thanks for the info guys my 40 year chiller god just retired and the new chiller guy is unsure about Tranes and I wanna take the bull by the horns but dont wanna create more problems , we have heat packs on all the smaller chillers just never done a oil change before .Thanks KnewYork that makes sence to me, was always to busy else where in the plant to have my retired friend show me . I have done leak checks with the heat packs but I also read in some other post the some people dont like to use heat packs cause it causes pressures on the o-rings and creats its own leaks .

  8. #8
    Join Date
    Jan 2011
    Posts
    1,170
    And Troy, my comment about "rocket science" was not directed at you. It was directed at milkyway for suggesting you had to get to Pro status before something as simple as removing oil from a low pressure centrifugal could be shared. I won't go in to technical detail on this open forum, but am willing to share common knowledge items with anyone who asks.

  9. #9
    Join Date
    Dec 2012
    Location
    Hamilton Ontario Canada
    Posts
    103
    Thanks again Knew York going to attempt first oil change tonight

  10. #10
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,059
    My first question to the OP would be why are you changing the oil in the first place ?
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  11. #11
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    KY
    What may be common knowledge to you may not be to others, the only reason I SUGGESTED to get pro status if one has never performed this they could be complications, example,.
    1. Over pressurize / loss of charge
    2. Accidentally interdiction of air

    If u wanted to share you great knowledge/ then share it but no need to call anyone out for someone suggest to apply for pro status-
    All I saw was a new guest status.

  12. #12
    Join Date
    Jan 2011
    Posts
    1,170
    Sorry I offended you milkyway.

  13. #13
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,095
    Troy. getting your post count up and applying for Pro membership is a good idea. We have a Pro only chiller forum that you may find very valuable sometime down the road.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event