  1. #1

    fouled evap water side

    I have a customer with and open loop titanium evap. After eliminating other possible issues have detemined evap to be fouled with algae/ slime/ snot whatever you care to call it. Upon open inspection of evap water side found significant white slime insulating evap tube bundle. What is the recommended treatment/ratio for cleaing/flushing. Have rotting/punched tooooo many condenser tube to fathom but usually the evap water side is closed loop and the water treatment company handles it. Not the case for commercial fish hatchery. recomendations please

  2. #2
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,041
    Tube cleaner, lots of brushes , pressure washer , and dont forget the PPE
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  3. #3
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,337
    I have brushed a few evaps. I clean them the same way as condensers.

  4. #4

    Brushes?????

    Quote Originally Posted by socotech View Post
    I have brushed a few evaps. I clean them the same way as condensers.
    Why would you brush the outside of a tube. Water typically flows thru a condenser tube so yes brush it by all means. But refrigerant flows thru the tubes in most evaps thus the need to rot the water side surrounding the tube bundle kinda hard to brush. Again I have Titanium tubes/ PVC shell trying to remove mainly algae......looking for best mixture ratio that will rinse clean when done. I need no trace chemicals when done as stated water flowing around the evap coil comes in direct contact with fish. Obviously I could run copper algaecide and it would remove the slime but what effect on the bundle??? Or simply acid??? But at what mixture. Typically we clean the inside of nickle copper condenser tube with acid. But this is a little different scenario.

  5. #5
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,020
    Many,many chillers have "flooded" evaporators, where the water is inside the tubes. Asking for help while "drip feeding" information wastes time. You should either be grateful that some are willing to waste their time, or you should give more complete information.

  6. #6
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Quote Originally Posted by Nuclrchiller View Post
    Many,many chillers have "flooded" evaporators, where the water is inside the tubes. Asking for help while "drip feeding" information wastes time. You should either be grateful that some are willing to waste their time, or you should give more complete information.
    Ya what this guy said. Oh and call the manufacturer and follow their recommendations.

  7. #7
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    874
    Many times when working through the various school districts in the Houston area I have found that due diligince was never accomplished when centrifigal chillers are started up and the welding slag started the corosion process. The chiller manufacturer never mattered Trane, York, Carrier or McQuay they all would foul the same. Solid black non-washable crap that had to be brushed with brass brushes after the tubes were rodded out. Even then it would always return to its fouled condition as we weren't allowed to attempt to clean the system. So, I would say get your PPE, tube brushing machine, brass brushes and grin and bear-it. -GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  8. #8
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,337
    P
    Quote Originally Posted by climate master View Post
    Why would you brush the outside of a tube. Water typically flows thru a condenser tube so yes brush it by all means. But refrigerant flows thru the tubes in most evaps thus the need to rot the water side surrounding the tube bundle kinda hard to brush. Again I have Titanium tubes/ PVC shell trying to remove mainly algae......looking for best mixture ratio that will rinse clean when done. I need no trace chemicals when done as stated water flowing around the evap coil comes in direct contact with fish. Obviously I could run copper algaecide and it would remove the slime but what effect on the bundle??? Or simply acid??? But at what mixture. Typically we clean the inside of nickle copper condenser tube with acid. But this is a little different scenario.
    I assumed you were talking about a flooded evap. By "rot", do you mean "rod"?

  9. #9
    Join Date
    Jan 2011
    Posts
    1,130
    Quote Originally Posted by Climate Master
    But refrigerant flows thru the tubes in most evaps...
    Maybe in your world. I've worked on far more flooded evaporator chillers than DX in my career. Maybe you could go purchase some of these and throw them in there. I understand they are really aggressive on algae.

  10. #10
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,334
    many 'small' chillers use a 'water on the outside / refrigerant on the inside' configuration for the evaporator.

    i guess you can try just about anything if they are going to not use proper water treatment. i understand that it will come in contact with live fish, however, even they need proper treatment too. if this is an on going problem, frequent drain down and aggressive cleaning and flushing may be in order.
    "Mother" is the name for God on the lips and hearts of children....The Crow

  11. #11
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    660
    Quote Originally Posted by KnewYork View Post
    Maybe in your world. I've worked on far more flooded evaporator chillers than DX in my career. Maybe you could go purchase some of these and throw them in there. I understand they are really aggressive on algae.
    Falling film also.
    X2 for the linked algae treatment.

    Have not laughed like this in days.

    Just an idea but you could sell them another pump and a plate heat-exchanger.
    Isolate the chiller to prevent further damage after cleaning.

  12. #12
    Join Date
    Dec 2011
    Posts
    107
    Open loop's should of had automatic tube cleaner installed from day one.

  13. #13
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    660
    Quote Originally Posted by steveoo View Post
    Open loop's should of had automatic tube cleaner installed from day one.
    Do they make automatic tube cleaners for chillers with water surrounding refrigerant tubes? Only ones I know of are the sponge balls that clean the inside of the tube.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event