    Quote Originally Posted by George2 View Post
    How do you highlight the sentences and put them in a box?

    Regarding the 600cfm to the second floor being enough, it must not be, he's hot.
    Although, it get worse, because he has only 5 supplies and who knows what size or how they are run. Plus, we just found out they are in the floor. That's the worst place to try and A/C a 2nd floor. I would like to see at least 2tons to that area.

    You can add return to the 2nd floor all day long and not make a difference if there is not enough supply. Again, assuming there is enough RA to the system now. And I would not take that bet.
    Regarding the 600cfm to the second floor being enough, it must not be, he's hot.
    Although, it get worse, because he has only 5 supplies and who knows what size or how they are run. Plus, we just found out they are in the floor. That's the worst place to try and A/C a 2nd floor. I would like to see at least 2tons to that area.

    You can add return to the 2nd floor all day long and not make a difference if there is not enough supply. Again, assuming there is enough RA to the system now. And I would not take that bet.

  2. #28
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,606
    Quote Originally Posted by George2 View Post
    Regarding the 600cfm to the second floor being enough, it must not be, he's hot.
    Although, it get worse, because he has only 5 supplies and who knows what size or how they are run. Plus, we just found out they are in the floor. That's the worst place to try and A/C a 2nd floor. I would like to see at least 2tons to that area.

    You can add return to the 2nd floor all day long and not make a difference if there is not enough supply. Again, assuming there is enough RA to the system now. And I would not take that bet.
    I don't have it yet.......I'm going to bed..........I'll try tomorrow.

  3. #29
    So I'm not seeing a consensus here...

  4. #30
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    933
    Quote Originally Posted by ThisOldFurnace View Post
    So I'm not seeing a consensus here...
    .

    You'll be old and grey before you do. You can create a poll.

    ..

    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  5. #31
    Join Date
    Apr 2008
    Location
    maryland
    Posts
    174
    Quote Originally Posted by ThisOldFurnace View Post
    So I'm not seeing a consensus here...
    If you want to go cheap try the manual dampers and use that 12x12 chase to install a return on the second floor in the ceiling. If only one return is going in a hallway you could also cut in pass through grills at the top of each wall adjacent to the hallway return in every room where there is a supply vent and keep the door closed you will then pressurise the room and hot humid air at the top of ceiling will then pass through the room and into the hallway where the main return is or just put a slightly smaller return in each room but thats not too cost effective. My two cents

    Sent from my DROID RAZR using Tapatalk 2

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event