    X-13 motor nitemare

    Anyone else having trouble with these x-13 gentech motors, all sizes so far that im seeing??

  2. #2
    Join Date
    Dec 2005
    Posts
    5,516
    Post Likes
    We've had a couple of threads on this in the past. In short, yes, many, many problems. Personally I only use PSC motors when I replace them.

  3. #3
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,900
    Post Likes
    Absolutely. I've replaced a TON. On all failures, check static pressure. I was told by my Carrier FSR that TESP should be below .6 to prevent failure.

    I was told that if they run over .6, the motor will fail in 12-18 months in humid climates (I.E. South Carolina, Georgia, Florida).

    All replacement modules should be remedied of this issue.