    AB Oil

    The company I'm working for is wanting us to come back in with AB Oil to replace the minerial oil on LT R22 Racks. Would it not be better to use POE ? Pros and Cons choosing one over the other would be great !!

    Thanks,

  2. #2
    Join Date
    Mar 2003
    Location
    Cochrane, AB
    Posts
    708
    Post Likes
    All the racks I work on were converted to AB many years ago. I think the biggest con against switching to POE is getting ALL the MO out. AB is much more forgiving. A pro would be that R22 is on it's way out and POE will be needed for the replacement refrigerant when the time comes. It's easier to take care of the oil conversion now, instead of both oil and gas later.

  3. #3
    Join Date
    Apr 2010
    Location
    San Diego, CA
    Posts
    236
    Post Likes
    Seems kinda late in the game to be just now switching out mineral oil no?

    I'd think that going to AB now would make the switch to POE later a bit smoother. I feel like MO to AB should be smooth, and then AB to POE should be fairly smooth as well, making the ultimate change to POE smoother overall, but I could be way off base.

  4. #4
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    change to poe oil. Don't worry about getting out all of the mineral oil. The oils will mix ok, and r22 is compatible with both of them.

  5. #5
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    I would do AB now and POE when nessisary. The AB will make the entire system look like a shinny new penny inside. So when you do switch to POE you'll have shinny clean system for that garbage to junk up.

  6. #6
    Join Date
    Mar 2003
    Location
    Cochrane, AB
    Posts
    708
    Post Likes
    Don't forget that many valves now have POE specific gaskets. Something else to consider is all the leaks after switching to POE.

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Switch to POE, then move into the compressor room for a couple weeks.

    That stuff will scrub out the system, far better than AB oil ever could.

    I'd also expect to do some valve rebuilds as the debris gets scrubbed loose and stuck in pistons, orifices and the like.


    I haven't seen leaks after the POE conversion, but the refrigerant conversion



  8. #8
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Switch to POE, then move into the compressor room for a couple weeks.

    That stuff will scrub out the system, far better than AB oil ever could.

    I'd also expect to do some valve rebuilds as the debris gets scrubbed loose and stuck in pistons, orifices and the like.


    I haven't seen leaks after the POE conversion, but the refrigerant conversion
    That's not all debtors plugging stuff up. Rebuilt a few economizers coated in what looks like cigarett tar but turned out to be POE not playing well with ANYTHING.

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Tommy knocker View Post
    That's not all debtors plugging stuff up. Rebuilt a few economizers coated in what looks like cigarett tar but turned out to be POE not playing well with ANYTHING.
    I've seen similar stuff come out of mineral oil systems.

    Low temp R-22 is H**L on oil



  10. #10
    Join Date
    Apr 2010
    Location
    Richmond, Virginia
    Posts
    388
    Post Likes
    Thread Starter
    Does copeland have a recommended oil to use when converting to R422 from R22 LT Rack!! ? Seems the best I have heard from the field when doning an oil change prior to the conversion it is best to do a mix of AB and Minerial oil and then when ready to do conversion drain all oil and then switch to the POE !!

  11. #11
    Join Date
    Feb 2007
    Location
    Deep South
    Posts
    355
    Post Likes
    I don't know about Copeland but Genetron R422C says it will work with MO AB or POE lubricants, hence no oil change.

    My experience tells me that the AB will have fewer oil return problems in your LT application.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •