  1. #40
    Join Date
    Feb 2008
    Location
    Tinley Park..ILLINOIS
    Posts
    5
    thanks , it was a single stage,the board had to be the problem all along finding the bad heat exchanger was a bonus

    Sent from my BlackBerry using Tapatalk please excuse typographical errors[/QUOTE]

  2. #41
    Join Date
    Jan 2006
    Location
    Northwest Missouri
    Posts
    252
    Just found one with a crack in the header,and a crack in the inducer bracket that hold the inducer motor will put pic on.

  3. #42
    Join Date
    Mar 2008
    Posts
    279
    Quote Originally Posted by eliteair View Post
    Just found one with a crack in the header,and a crack in the inducer bracket that hold the inducer motor will put pic on.
    That is pretty common with tranes design and first thing I check. But my photos where a result of hairline cracks in the secondary plastic collector box. Only way to see it was to pull it, not sure if u could see the detail needed with a snake camera but I would like to try.

    Sent from my BlackBerry using Tapatalk please excuse typographical errors
    If you can not do it right, Why even do it at all?

  4. #43
    Join Date
    Dec 2012
    Location
    Columbus OH
    Posts
    32
    Yes I have noticed them with pin holes ,heat exchangers aren't mad like they used to be and the manufacture doesn't carry the 20 yrs like they use to ..Regards

  5. #44
    Join Date
    Mar 2008
    Posts
    279
    Quote Originally Posted by techwizard007 View Post
    Yes I have noticed them with pin holes ,heat exchangers aren't mad like they used to be and the manufacture doesn't carry the 20 yrs like they use to ..Regards
    I am not sure everyone here would agree with me but why not spend a couple extra dollars and make that cover out of stainless or anything other then plastic and I wonder if they would not be having this issue anyone else fell this way?

    Sent from my BlackBerry using Tapatalk please excuse typographical errors
    If you can not do it right, Why even do it at all?

  6. #45
    Join Date
    Jan 2008
    Location
    s chester county,pa
    Posts
    144
    had one today that was leaking water on the right hand side above the blower motor in blower compartment.(tux080c942c3) i think its the inducer. alot of sloshing on startup.unit plumb and level. upflow.drains and traps clear. please advise if im wrong. rescheduled pulling inducer and gasket replacement. all ca readings were good. 0ppm in home

  7. #46
    Join Date
    Dec 2011
    Location
    Twin Cities Minnesota
    Posts
    224
    Hey Techwiz...,Goodman has a lifetime on there H.X.

  8. #47
    Join Date
    Jul 2012
    Location
    Cincinnati ohio
    Posts
    252
    Quote Originally Posted by Cosmicmuffin View Post
    Hey Techwiz...,Goodman has a lifetime on there H.X.
    Most manufacturers have a 20 year or lifetime warranty. certain carrier models have only a 10 year.

  9. #48
    Join Date
    Jul 2012
    Location
    Cincinnati ohio
    Posts
    252
    Quote Originally Posted by 2141 View Post
    It doesn't matter the model. I have seen them on every model both 80 and 90 %. Here is a picture I took using my see snake and phone. It right underneath the burner entry Attachment 335651
    Has anyone found any of these lately?

  10. #49
    Join Date
    Jun 2009
    Location
    Northwest IN/Chicago
    Posts
    268
    Good lord, glad I found this thread! This answers my question about how Trane HX's are holding up... Now i'll be keeping an eye out.

    Are these failing HX's you guys are finding not getting enough airflow or something? (in other words any of them fail with proper airflow/ductwork etc)

  11. #50
    Join Date
    Jul 2012
    Location
    Cincinnati ohio
    Posts
    252
    Quote Originally Posted by Gus-Herb94 View Post
    Good lord, glad I found this thread! This answers my question about how Trane HX's are holding up... Now i'll be keeping an eye out.

    Are these failing HX's you guys are finding not getting enough airflow or something? (in other words any of them fail with proper airflow/ductwork etc)
    There is no reason outside of design or quality of materials.

  12. #51
    Join Date
    Apr 2012
    Location
    Cleveland
    Posts
    605
    Name:  ImageUploadedByTapatalk 21360888443.635084.jpg
Views: 380
Size:  37.6 KB

    Found this one today. 9 yrs old.

  13. #52
    Join Date
    Mar 2008
    Posts
    279
    Quote Originally Posted by Hvac216 View Post
    Name:  ImageUploadedByTapatalk 21360888443.635084.jpg
Views: 380
Size:  37.6 KB

    Found this one today. 9 yrs old.
    I assume that is the tail piece from secondary to comb blower motor?

    Sent from my BlackBerry using Tapatalk please excuse typographical errors
    If you can not do it right, Why even do it at all?

Page 4 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event