Has anyone else had an issue with trane heat exchangers? We are coming across about five a day. These furnaces are on average 3 years old and up.
Has anyone else had an issue with trane heat exchangers? We are coming across about five a day. These furnaces are on average 3 years old and up.
Yes I have. Their all cracking at the collector box. If you notice rust on the screws at the bottom then its cracked.
The secondarys crack easily seen behind the transition receptacle for the inducer but those are not the cracks I'm talking about. the cracks I was mainly referring to are underneath where the flame enters, on the left side of each chamber, off the top of the crimp. I think the altitude is 2000
Altitude will make a difference on a hotspot. The code where I live [4.22.1] in Ontario references CSA/CGA 2.17 and states "...it shall be adjusted to the high-altitude rating shown on the nameplate when installed at elevations between 2000ft and 4500ft above sea level." This is quoted from CSA-B149.1-10.
The furnace should be derated on install. There should be a manifold pressure given on the nameplate for that elevation. Beyond 4500ft, it is 4% for every 1000ft in elevation....a way to verify derating is to clock the meter. 1 cu.ft = 1000BTU (roughly) as you may know.
HVAC-Talk has a thread referencing derating....
http://hvac-talk.com/vbb/showthread.php?75461-Question-about-derating-gas-furnace-for-altitude
Hey mod....where's the love? Make me a pro member already
Yeah problems with Tranes of all sizes, crappy material used to make the exchanger.
This is scary, we have been a trane dealer around 3 years. Is there a recall or anything?
Wow that's bad, the most expensive equipment on the market is bad. Is it all HXs or does is seem to be a certain model?
It doesn't matter the model. I have seen them on every model both 80 and 90 %. Here is a picture I took using my see snake and phone. It right underneath the burner entry
On a pm today, this was installed a year ago, inducer sprung a leak.
Great pic...thanks. It would be a hard sell on water marks and corrosion alone to a home owner. Do you have any additional information? Flame? Drainage? Rollouts? It would be great to get a pic of the ruptured heat exchanger. Cutting a piece out the side would be proof beyond a reasonable doubt.....That is, if you're tagging the furnace.
Here's one I had recently......the flame wasn't right and I hadn't noticed the metal chips until removing the burners.....it verified what I couldn't easily see. The original issue was a rollout switch tripping. It's fortunate this issue was found before a fatality.
Joehvac25, how can you tell?
Thanks