Page 1 of 3 123 LastLast
Results 1 to 13 of 36
  1. #1

    Flooded Two Pipe Steam System

    A bypass valve on the feedwater line was opened by a janitor. The entire system flooded, two floors. We drained all the water we could at the boiler. Fired the boiler back up and began making steam. The problem is we are not getting hot through atleast half the building. The system was working fine before the flood. No cool spots and everyone was happy. What should be my next course of action? Haven't run into this problem before.

  2. #2
    Join Date
    Mar 2011
    Location
    North Carolina Piedmont Area
    Posts
    309
    Have you verified that the air has been removed from the system. Steam will not travel down the line if air is in the system.

    Have you checked that air vents are working correctly. How about the steam traps.
    How many floors are in the building.
    What is the the steam pressure in the system.
    How large is the boiler or BTU rating.
    Is there a condensate pump in place and possibly a receiver.

  3. #3
    Join Date
    Nov 2004
    Location
    Western NY
    Posts
    984
    Quote Originally Posted by jodaddy1956 View Post
    A bypass valve on the feedwater line was opened by a janitor. The entire system flooded, two floors. We drained all the water we could at the boiler. Fired the boiler back up and began making steam. The problem is we are not getting hot through atleast half the building. The system was working fine before the flood. No cool spots and everyone was happy. What should be my next course of action? Haven't run into this problem before.
    thats is very weird! cause the boiler water level is controlled by a float that turns on/off the feed water pump, opening the bypass valve would overflow the condensated receiver not the boiler.

  4. #4
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    2,104
    Quote Originally Posted by valdelocc View Post
    thats is very weird! cause the boiler water level is controlled by a float that turns on/off the feed water pump, opening the bypass valve would overflow the condensated receiver not the boiler.
    I have seen where they have piped a bypass right to the boiler. Stupid but they are out there.


    Sent from my iPad using Tapatalk HD
    To the man who always did it right. I love you dad and I will miss you to much for words.


    Stay Thirsty My Friends


    Support the Skilled Trades Don't DIY

  5. #5
    Join Date
    Nov 2004
    Location
    Western NY
    Posts
    984
    Quote Originally Posted by qwerty hvac View Post
    I have seen where they have piped a bypass right to the boiler. Stupid but they are out there.


    Sent from my iPad using Tapatalk HD
    What kind of bypass you taking about? I'm taking about the make up water solenoid bypass, when the water level gets low in the receiver the float powers the solenoid valve allowing street water into the tank.
    I have never seen a commercial steam boiler with cold make up water piped directly into the boiler. next time you come across one please take a picture.

  6. #6
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    2,104
    Quote Originally Posted by valdelocc View Post
    What kind of bypass you taking about? I'm taking about the make up water solenoid bypass, when the water level gets low in the receiver the float powers the solenoid valve allowing street water into the tank.
    I have never seen a commercial steam boiler with cold make up water piped directly into the boiler. next time you come across one please take a picture.
    I have seen a few where they pipe it right to the boiler with a valve. I figured it was to fast fill it after it has been drained. Normally I will see a bypass around the PRV. But these were piped after the PRV bypassing the condensate tank. I will take a pic of the on I am thinking about if I go there again. I can see if someone didn't know what valve they were opening filling the whole system.


    Sent from my iPad using Tapatalk HD
    To the man who always did it right. I love you dad and I will miss you to much for words.


    Stay Thirsty My Friends


    Support the Skilled Trades Don't DIY

  7. #7
    Join Date
    Nov 2004
    Location
    Western NY
    Posts
    984
    Quote Originally Posted by qwerty hvac View Post
    I have seen a few where they pipe it right to the boiler with a valve. I figured it was to fast fill it after it has been drained. Normally I will see a bypass around the PRV. But these were piped after the PRV bypassing the condensate tank. I will take a pic of the on I am thinking about if I go there again. I can see if someone didn't know what valve they were opening filling the whole system.


    Sent from my iPad using Tapatalk HD
    That brings another question, why would a PRV be needed in a condensated receiver? I'm use to see PRV's with hot water boilers no with steam cause the water pressure is pretty much irrelevant.

    Also if the make up water was piped directly into the boiler, the street pressure 40lb to 80lb would had been higher than the 15LB opening pressure of the boilers relief valve, the whole scenario is flawed and weird, dont you think?

  8. #8
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    3,028
    I've heard of some systems use pressure differential to lift water out heaters below the condensate line. if they're full of water, steam would not be able to clear lines of the water.

    water in rads/traps holding the thermostatic elements closed?
    Col 3:23


    questions asked, answers received, ignorance abated

  9. #9
    Join Date
    Dec 2006
    Location
    new england
    Posts
    481
    I changed out a makeup water float assembly on a 50 gallon condensate receiver last friday. I believe it was a Hoffman. The tank nameplate said max inlet water pressure was 30 psi and a prv would need to be installed if water pressure was higher.
    Chaos equals cash$$$

  10. #10
    Join Date
    Jun 2006
    Posts
    249


    Pretty much every commercial boiler I've come across in NYC has a city water feed piped directly to the boiler. The pipe with the green arrows is the city water feed.

  11. #11
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    2,104
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1356658404.442206.jpg 
Views:	113 
Size:	40.6 KB 
ID:	340711Click image for larger version. 

Name:	ImageUploadedByTapatalk1356658416.241167.jpg 
Views:	125 
Size:	56.5 KB 
ID:	340721

    Here is one that I was talking about. PRV on the makeup water.


    Sent from my iPhone 4s
    using Tapatalk
    To the man who always did it right. I love you dad and I will miss you to much for words.


    Stay Thirsty My Friends


    Support the Skilled Trades Don't DIY

  12. #12
    Join Date
    Apr 2004
    Location
    Maryland
    Posts
    521
    I see it all the time. When you drain a large boiler for inspection you can use the feed to refill the boiler on initial startup. Otherwise you will have to fill with your pump from the condensate receiver tank. On a 300-400 HP boiler that can take a while, I usually fill to the sight glass with the city water supply then valve it off and let the low water cut off fill the rest of the way with the condensate pump.

  13. #13
    Join Date
    Nov 2004
    Location
    Western NY
    Posts
    984
    Quote Originally Posted by marylandtech View Post
    I see it all the time. When you drain a large boiler for inspection you can use the feed to refill the boiler on initial startup. Otherwise you will have to fill with your pump from the condensate receiver tank. On a 300-400 HP boiler that can take a while, I usually fill to the sight glass with the city water supply then valve it off and let the low water cut off fill the rest of the way with the condensate pump.
    No a common practice in my neck of the woods, typically the make up (street) water, goes through the filters,softener and to the condensate receiver. I wouldn't put raw,untreated water in,and wouldnt pipe it directly into the boiler for the obvious reason.