    Flooded Two Pipe Steam System

    A bypass valve on the feedwater line was opened by a janitor. The entire system flooded, two floors. We drained all the water we could at the boiler. Fired the boiler back up and began making steam. The problem is we are not getting hot through atleast half the building. The system was working fine before the flood. No cool spots and everyone was happy. What should be my next course of action? Haven't run into this problem before.

  2. #2
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    Have you verified that the air has been removed from the system. Steam will not travel down the line if air is in the system.

    Have you checked that air vents are working correctly. How about the steam traps.
    How many floors are in the building.
    What is the the steam pressure in the system.
    How large is the boiler or BTU rating.
    Is there a condensate pump in place and possibly a receiver.

  3. #3
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,819
    Post Likes
    Quote Originally Posted by jodaddy1956 View Post
    A bypass valve on the feedwater line was opened by a janitor. The entire system flooded, two floors. We drained all the water we could at the boiler. Fired the boiler back up and began making steam. The problem is we are not getting hot through atleast half the building. The system was working fine before the flood. No cool spots and everyone was happy. What should be my next course of action? Haven't run into this problem before.
    thats is very weird! cause the boiler water level is controlled by a float that turns on/off the feed water pump, opening the bypass valve would overflow the condensated receiver not the boiler.

  4. #4
    Join Date
    Mar 2010
    Location
    Tidewater Virginia
    Posts
    140
    Post Likes
    Quote Originally Posted by valdelocc View Post
    thats is very weird! cause the boiler water level is controlled by a float that turns on/off the feed water pump, opening the bypass valve would overflow the condensated receiver not the boiler.
    Some systems use float style mechanical water makeup directly into the boiler jacket rather than injecting into the condensate return tank and being pumped into the boiler with the returning condensate.

  5. #5
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,819
    Post Likes
    Quote Originally Posted by bearfromobx View Post
    Some systems use float style mechanical water makeup directly into the boiler jacket rather than injecting into the condensate return tank and being pumped into the boiler with the returning condensate.
    Weird that anyone would pipe cold make up water direct to the boiler, it doesn't make sense and seems kind of dangerous. I work on 50 to 500hp steam boilers and I dont recall ever seeing one piped that way, I have also never seeing a boiler flying through the roof at 250mph and like to keep it that way.

  6. #6
    Join Date
    Mar 2010
    Location
    Tidewater Virginia
    Posts
    140
    Post Likes
    Name:  Series47.jpg
Views: 65
Size:  2.9 KB

    Quote Originally Posted by valdelocc View Post
    Weird that anyone would pipe cold make up water direct to the boiler, it doesn't make sense and seems kind of dangerous. I work on 50 to 500hp steam boilers and I dont recall ever seeing one piped that way, I have also never seeing a boiler flying through the roof at 250mph and like to keep it that way.
    This is a photo of a Hoffman Series 47 water feeder and low water safety device, often found on smaller boilers and sometimes piped with a bypass "fast flood" valve around the fill valve. For gravity return systems, it's outlet is near piped at the condensate return conection or into the boiler jacket. it doesn't feed a lot of water at a time but I agree with you that tempering the water by mixing with the condensate is a much better idea where it works. If a 50 HP is as small as you work on, I doubt you see many gravity returns.

    And Yes, I agree that the first boiler I see leave it's pad is one too many. My underwear will look like I hit a deer!

  7. #7
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Quote Originally Posted by valdelocc View Post
    thats is very weird! cause the boiler water level is controlled by a float that turns on/off the feed water pump, opening the bypass valve would overflow the condensated receiver not the boiler.
    I have seen where they have piped a bypass right to the boiler. Stupid but they are out there.


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  8. #8
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,819
    Post Likes
    Quote Originally Posted by qwerty hvac View Post
    I have seen where they have piped a bypass right to the boiler. Stupid but they are out there.


    Sent from my iPad using Tapatalk HD
    What kind of bypass you taking about? I'm taking about the make up water solenoid bypass, when the water level gets low in the receiver the float powers the solenoid valve allowing street water into the tank.
    I have never seen a commercial steam boiler with cold make up water piped directly into the boiler. next time you come across one please take a picture.

  9. #9
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Quote Originally Posted by valdelocc View Post
    What kind of bypass you taking about? I'm taking about the make up water solenoid bypass, when the water level gets low in the receiver the float powers the solenoid valve allowing street water into the tank.
    I have never seen a commercial steam boiler with cold make up water piped directly into the boiler. next time you come across one please take a picture.
    I have seen a few where they pipe it right to the boiler with a valve. I figured it was to fast fill it after it has been drained. Normally I will see a bypass around the PRV. But these were piped after the PRV bypassing the condensate tank. I will take a pic of the on I am thinking about if I go there again. I can see if someone didn't know what valve they were opening filling the whole system.


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  10. #10
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,819
    Post Likes
    Quote Originally Posted by qwerty hvac View Post
    I have seen a few where they pipe it right to the boiler with a valve. I figured it was to fast fill it after it has been drained. Normally I will see a bypass around the PRV. But these were piped after the PRV bypassing the condensate tank. I will take a pic of the on I am thinking about if I go there again. I can see if someone didn't know what valve they were opening filling the whole system.


    Sent from my iPad using Tapatalk HD
    That brings another question, why would a PRV be needed in a condensated receiver? I'm use to see PRV's with hot water boilers no with steam cause the water pressure is pretty much irrelevant.

    Also if the make up water was piped directly into the boiler, the street pressure 40lb to 80lb would had been higher than the 15LB opening pressure of the boilers relief valve, the whole scenario is flawed and weird, dont you think?

  11. #11
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    4,485
    Post Likes
    I've heard of some systems use pressure differential to lift water out heaters below the condensate line. if they're full of water, steam would not be able to clear lines of the water.

    water in rads/traps holding the thermostatic elements closed?
    Col 3:23


    questions asked, answers received, ignorance abated

  12. #12
    Join Date
    Dec 2006
    Location
    new england
    Posts
    751
    Post Likes
    I changed out a makeup water float assembly on a 50 gallon condensate receiver last friday. I believe it was a Hoffman. The tank nameplate said max inlet water pressure was 30 psi and a prv would need to be installed if water pressure was higher.
    Chaos equals cash$$$

  13. #13
    Join Date
    Jun 2006
    Posts
    366
    Post Likes


    Pretty much every commercial boiler I've come across in NYC has a city water feed piped directly to the boiler. The pipe with the green arrows is the city water feed.