    Spyder and VariTrane

    Has anyone had issues with Spyders retrofitted to Trane VariTrane Vav's?

    We did a buidling with 72 of these Vav's. We landed the actuators directly to the BO's. We are now having issues with the triac's. The current of the actuators are below the rating of the triacs.

    We are planning on installing relays, but it's going to be a major lose to the project now. I have another building with the same Vav's with XL10's and no problems, but the triacs are on the common side....not the 24v side.

  2. #2
    Join Date
    Mar 2011
    Location
    North Carolina Piedmont Area
    Posts
    452
    The synchronized type motor use's the same common which I am sure you know. The installation of relays should work as it will isolate the circuits.

  3. #3
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    1,708
    Hmm...I did a job with about 50 of them a couple of years ago and have not had any problems. The actuators are connected directly to the spyders.
    Go Rangers!

  4. #4
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,340
    I have the triac's either failing open or closed. I hook up a relay on a few just to see what's going on.

    Here's one-
    http://s238.beta.photobucket.com/use...V_2_2.mp4.html

  5. #5
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    1,708
    Are you sure they are not out of synch? Don't those actuators have like a 5 minute drive time?

  6. #6
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,340
    I have them set up with a 6 minute stroke time.

    In the video, you can see that DO7(Open) have fail closed all the time. I have others were I lost DO8(Close). And some triacs have failed closed, while others have failed open

  7. #7
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    1,708
    I could'nt get the video to work.
    Go Rangers!

  8. #8
    Join Date
    Nov 2007
    Location
    Clayton, NC
    Posts
    42

    Spyder and Varitrane

    I retrofitted a building with about 120 varitranes a couple of years ago using Trend's IQ-eco vav controller which looks identical to a Honeywell spyder (both made by Honeywell). I used the triacs directly to the trane actuators and after a year about 15 or so triacs had failed as you described. These were older varitranes. It was my best guess that when the worn out gears of some the varitranes would get in a bind, they would over amp the triacs. I have made it a point since then to always put pilot relays on these types of retrofits to isolate the triacs.

  9. #9
    Join Date
    Mar 2011
    Location
    North Carolina Piedmont Area
    Posts
    452
    The synchronized motors draw 0.37 AMPS to open and close. The close motor has a small capacitor to assist.

  10. #10
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,340
    I little update from a 1.5 years ago........the video is beat, at this point.

    But we finally found the problem and the solution.

    We have been installing isolation relays and switching DO's on failure. Which has been working, but no reason why. So I come across a document, today that explains everything.

    Thought I would share.

    C11-001 Series 60 VC actuators with limit switches causing Triac failures.pdf

  11. #11
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    1,016
    Thanks for the info.

  12. #12
    Join Date
    Nov 2007
    Location
    Clayton, NC
    Posts
    42
    Thanks for this post. Glad to see some resolve to this issue. I may try out this solution on the job I posted about that does not have the isolation relays. I've lost a few more triacs here since I posted in December.