Interpret my static air pressure numbers
Today I ran a system check on my furnace for the first time, a Carrier 80% two stage (54k btu output on high and 36 k output on low, oversized I know, but about as small as I could get, and probably does not matter much as the heat pump generally runs except during morning warmup) installed with a two ton heat pump for dual fuel. It has an infinity thermostat and reports air flow cfm, motor rpm, and static pressure.
First, are the numbers reported by the system generally reliable? Do ya'll go by them when they are available on the thermostat, or do you always take your own readings?
My numbers were
Low heat: Air flow 633 cfm, motor rpms maxed out at 654, and static pressure bounced between .27 and .28.
High heat: Air flow 1033 cfm, motor rpms 1133, and static pressure of .78.
Are these normal, acceptable numbers?
Thanks
-
11-30-2012, 11:20 PM #2
they are good. you only need 800cfm for high fire. i would have a professional lock it in hi fire and lower airflow to ~ 800cfm. this will save you in fuel consumption and heat your house quicker.
-
12-01-2012, 10:57 AM #3
Regular Guest
- Join Date
- Jun 2010
- Location
- Charlotte, NC
- Posts
- 155
Thanks, I did not know I could do that. It sounds like good advice.
I understand why locked into high fire would be economical, but why do I want to lower the cfms? Just wondering what the theory is behind it.
Thanks
-
12-01-2012, 01:53 PM #4
-
12-01-2012, 01:59 PM #5
-
12-01-2012, 02:06 PM #6
If the system is oversized for heating. I would not expect the 2nd stage heat to come on unless you raise the temp on t-stat 10 degrees above set point. That is a very advanced system with many options and settings.
Best thing to do is let the installer review over it and make changes for you. It could just be a simple setting that needs to be changed for better comfort. I agree with Beenthere, 2nd stage numbers look high by reducing the cfm down will allow for more even temps and want run such high static.
-
12-01-2012, 02:17 PM #7
so you have a 60,000btu furnace. 54,36
If the furnace was tuned to get the max btus then you would have ~ 54,000 output. 54,000/70,000input = 80% efficient
now low fire; 36,000/70,000 = 51% efficient.
high fire runs at 5 mins to heat the house
low fire runs at 15 mins to heat the house
i wonder which one is cheaper to run?
now if you like longer run times with lower temp coming out the registers then go ahead with the 2 stage.
if you want to save money and have hot air coming out, then keep it in high fire or get a single stage furnace.
-
12-01-2012, 03:00 PM #8
.78 is terrible. .28 is awesome. Going a step further, probably easiest to simply lock out high fire. Slowing airflow at a stage reduces transfer efficiency X heat exchanger.
Gravity may have recently taken a course that obsesses on combustion efficiency. These courses emphasize combustion efficiency as if it is the prime determinant in efficiently replacing heat loss. Usually takes about a year to correct the dogmatic and myopic perspective indoctrinated by these classes.
Efficiency is maximized by keeping occupants comfortable, not by obsessing on a point or two of combustion efficiency (at steady state). High fire is often impediment to achieving comfort.Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.
-
12-01-2012, 03:19 PM #9
Comfort and Efficiency are two totally different things.
Efficiency is maximized by inputting and outputting what the appliance is designed to do!
Comfort is about keeping a homeowner comfortable.
You could have a very undersized furnace that is putting out its maximum efficiency but not keeping the customer comfortable.
Give it time. People will start to become aware of these energy wasting furnaces.
Or people who monitor their fuel bills will notice the bill getting higher with their new 98%AFUE furnace. Which is nearly impossible to get 98% efficiency out of a furnace. 88% is the maximum you can get out of a furnace.
-
12-01-2012, 06:04 PM #10
Regular Guest
- Join Date
- Jun 2010
- Location
- Charlotte, NC
- Posts
- 155
In this case and for my specific application, I agree with Gravity, even over Beenthere and Tedkidd, both of whom I respect very much and have learned a lot from.
The reason is that I like to do a night setback and drop the temp from 71 to 65 overnight. Most nights the temp only drops to 66-68 overnight, though on very cold nights it will go down to 65 by morning.
When I have the system kick back on, at 5:30 in the morning, 15 minutes before my son has to get up for high school, I want the house to warm up fast and that is when the heat pump is at its least efficient, it being cold outside. So I would be glad for the furnace to come on high fire to get it quickly back to 71. Once it does, the two ton heat pump will take over for the rest of the day and provide slow even cost-effective heat all day.
Right now the furnace runs about twice as often in low stage as in high, and I would prefer it to be locked in high to get maximum efficiency for that short period of time in the morning the furnace runs.
My manual J had my heat loss at design conditions to be 34,000. So it is true I could get by with only low stage, but why use the furnace at its least efficient?
On the other hand, I would like to have low stage furnace come on during those coldest nights when the indoor temp does dip below 65 overnight. Wonder if I can program it to do that while always going to high fire when during morning warm up.
-
12-01-2012, 07:42 PM #11
-
12-01-2012, 07:46 PM #12
Get a Honeywell IAQ thermostat then. It can control both stages of your gas furnace. Coming out of set back it will use second stage. On normal days/nights when the heat pump and first stage can't keep up, it will know to use second stage. Giving you long run times in first stage, and going to second stage if need be. No sudden temp swings. All other times it will use the heat pump or just first stage of the gas furnace.
If you use AI recovery, it will start to heat teh house up early, and may not even have to use second stage.
-
12-01-2012, 10:12 PM #13
Gravity, I won't be telling you how to install and commission furnaces. You would make me look quite the fool. Might want to be careful talking about how to save money on energy...
THE BEST WAY TO ACHIEVE AMAZING EFFICIENCY IS TO DESIGN FOR COMFORT. Your orientation is 180 degrees off. Fact is, the more I have focused on effectively making occupants comfortable, the more surprised I am by the energy savings.
The idea comfort is achieve by brute force makes unable think properly about delivering both impossible. That's exactly what most traditional - old school thinking - hvac guys think. I see it here and in my area every day. They look at one link and forget the whole rest of the chain.
There is a new school group of HVAC guys who are beginning to understand that hammers are not always the best solutions, and all problems are not nails. They are recognizing the furnace is just a small link in the chain, unless you get it wrong.
These are HVAC guys that are turning into building scientists. This is an often painful transition, it requires recognizing that a lot of what came before was done terribly wrong. But something done wrong due to incomplete information is an unavoidable fact of life. Humans simply aren't perfect. Furthermore, knowledge and science are not static!
Doing something you later learn was wrong is not the same as doing something wrong once you know better. Everybody has over sized equipment. We did not know better. But once enough people in the field start telling you the old ways are wrong, you can no longer claim ignorance.
HVAC guys turned building scientist will OWN this new field.
It is geometrically easier to jump into the envelope side of this business from hvac than it is to go from envelope TO hvac. The ability to understand technical issues is something HVAC guys, by their nature, can handle. A guy holding a hose blowing cellulose, maybe not so much. I know I'd rather have an HVAC guy running around my home with caulk than a spray foam guy hooking up gas pipe.
I've seen people try both jumps. Some fail, some succeed. The HVAC guys succeed probably 10 to 1 over the envelope guys. Wanna see a hack job? Check out a furnace installed by an envelope guy.
You've swallowed the dogmatic bs deep, it'll may be difficult to get that hook out.
Unfortunately very few furnace guys get energy the way wetheads get it, no wethead would lock a modcon on high fire. They'd think you were completely nuts, and possibly stop wasting their breath. Fluid dynamics and thermodynamics apply to water and air.
Here's some more stuff by Robert Bean to look at, maybe we can dislodge that hook:
High fire, quick recovery is NOT the way to achieve low return temperatures. Wetheads know this, and a few furnace guys.For example, a 98% efficient boiler only achieves such high performance when it operates at low temperatures typically below 80 deg F (27 deg C).
Regardless of the use of programmable thermostats, when a 98% efficient boiler is run at 180 deg F (82 deg C) it still only achieves a nominal 85%.
http://www.healthyheating.com/Boiler...m#.ULrD-KzBG84Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.