    Rheem/Ruud TEV Issues

    Anyone having TEV issues with Rheem or Ruud units?
    The problem revolves around the TEV (Thermostatic expansion valve) valves sticking closed and starving the evaporator causing it to freeze and possibly damaging the compressor.
    We installed a new unit for a customer and are installing a new TEV on the unit for the third time. We have asked our supplier (Gemaire) to replace the unit as its had on going failures of the TEV since new. (2 months). They flat out said NO.
    After several calls to Rheem/ Ruud to address the problem they have failed to return any calls regarding this issue.
    Keep i mind they have an issue with their units and continue selling them everyday even when they don't know the cause.
    We are going to have to replace the unit for our customer at our expense.
    It wont let me upload the notice from Rheem/Ruud about the issue.............

  2. #2
    Join Date
    Apr 2013
    Location
    In my head
    Posts
    309
    Wow, 3 TX valves failing in a row? What are the chances?!

  3. #3
    Join Date
    Jul 2003
    Location
    Virginia Beach
    Posts
    153
    Factory contamination issue, wish i could upload the memo from Rheem/Ruud that came out today.

  4. #4
    We were told by AC service company the valves are being clogged by an anti-corrosive protective coating on the condenser. The problem affects model 13AJN048 with Copeland scroll compressors. The valve must be replaced once it is clogged.

    Has anyone had this problem?

  5. #5
    Join Date
    Jan 2002
    Posts
    253
    Quote Originally Posted by FloridaPM View Post
    We were told by AC service company the valves are being clogged by an anti-corrosive protective coating on the condenser. The problem affects model 13AJN048 with Copeland scroll compressors. The valve must be replaced once it is clogged.

    Has anyone had this problem?
    http://www.emersonclimate.com/en-us/...te-8-28-14.pdf

    As mentioned check with tech support from your manufacturer. Different companies doing different repairs from replace gas valve etc to just put some Koolaid juice in it. They will probably pay you for your work too. If they don't start installing a different brand.
    Two wire hook up, three wire f**k up.

  6. #6
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,158
    As the bulletin says, usually failures are with 3 ton and under units.

    Sent from my HTC VLE_U using Tapatalk

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event