  1. #27
    the "saga" continues, received the secondary yesterday, so we proceeded to change it today when I pulled it out I found 2 rings from the clam shell of the primary and proceeded to pull that out and visually inspected found a total of 6 rings busted out, so the primary will have to be replaced. Then I needed to make sure the secondary is in fact cracked or leaking and the only thing I could think of doing was to stand it with the bends towards the bottom and fill the tubes with water and let it sit for a while and had no water leakeage at all now the dillema is where was the water coming from? and obviusly why wasn't my combustion analizer registering CO in the conditioned air dam thing is brand new and for $2K you'd think it be calibrated..........
    Last edited by frustraded tech; 12-14-2012 at 06:53 PM. Reason: grammar

  2. #28
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,068
    Quote Originally Posted by frustraded tech View Post
    the "saga" continues, received the secondary yesterday, so we proceeded to change it today when I pulled it out I found 2 rings from the clam shell of the primary and proceeded to pull that out and visually inspected found a total of 6 rings busted out, so the primary will have to be replaced. Then I needed to make sure the secondary is in fact cracked or leaking and the only thing I could think of doing was to stand it with the bends towards the bottom and fill the tubes with water and let it sit for a while and had no water leakeage at all now the dillema is where was the water coming from? and obviusly why wasn't my combustion analizer registering CO in the conditioned air dam thing is brand new and for $2K you'd think it be calibrated..........
    An analyzer will not pick up CO in the supply air when the heat exchanger is cracked. There is nothing wrong with the analyzer, don't bother testing the supply air for CO, it doesn't tell you anything about how safe the furnace is.

  3. #29
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    402
    6 busted rings and it wasn't noticed on the first visit, this is why when I go to a new customer they get upset when I find stuff like that and they say it gets checked every year. Thank you for all the loyal customers they're the ones that don't get estimates from other companies and they stay with us forever.

  4. #30
    it always did in the past same analizer model, has a screen for flue and conditioned air. selection for gas type etc...

  5. #31
    it's not like i didn't test for it, that has been my diagnosis from the begining but I frustrated because could not prove or document it!

  6. #32
    Join Date
    Nov 2012
    Location
    Georgia
    Posts
    13
    Just a thought...I have seen faulty roll out switches. I had a 90plus furnace kick my butt for a week, changed the switch and never had another issue with it. Luckily it was a friends system.

  7. #33
    Try measuring the temps at the roll out It shouldnt be even close to the trip temp

  8. #34
    Roll out switch tripping on the H9mpd series furnaces is usually the result of a problem with the secondary heat exchanger. There was a problem with the oil used when the heat exchanger was formed. It would react with acid from the flue gases and form a thick sludge that pluged the tubes in the exchanger. It required removal of the cold header box and the turbulators and then working a wire with a rag attached thru each tube till they were clear. A messy and time consuming job but it would get the furnace working. Worse case would be a cracked secondary heat exchanger although I have not found one yet.

  9. #35
    we found 6 rings busted out, plus first post explained that we switched the roll-outs and the unit kept tripping on the same spot not the switch.

  10. #36
    upon inspection this exchanger was very clean small buildup @ the bottom where the transfer box to the secondary bolts on.

  11. #37
    this particular unit did not have any sludge what so ever!

  12. #38
    Join Date
    Nov 2011
    Location
    Philadelphia, PA
    Posts
    195
    Quote Originally Posted by frustraded tech View Post
    the "saga" continues, received the secondary yesterday, so we proceeded to change it today when I pulled it out I found 2 rings from the clam shell of the primary and proceeded to pull that out and visually inspected found a total of 6 rings busted out, so the primary will have to be replaced. Then I needed to make sure the secondary is in fact cracked or leaking and the only thing I could think of doing was to stand it with the bends towards the bottom and fill the tubes with water and let it sit for a while and had no water leakeage at all now the dillema is where was the water coming from? and obviusly why wasn't my combustion analizer registering CO in the conditioned air dam thing is brand new and for $2K you'd think it be calibrated..........
    Just cause you have a crack doesn't mean co in condition space

  13. #39
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    154
    CO rots steel! Any CO. If you have pulled a water heater burner covered with flakes of rust, you have seen CO at work. I concur with the flakes in the secondary. ALSO; you mentioned the Delta T being high. Perhaps a restricted duct? What is the External static on the system?

    Quote Originally Posted by frustraded tech View Post
    sorry, forgot to mention that has been done the flue readings where about 89% efficiency 122F & 6.2 CO

Page 3 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event